Thread: in line fuse holder

  1. #1
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,619

    in line fuse holder

    I need/want some inline fuse holders, supplementary, that can be used at each 480v fixture.

    Suggestions?
    Tom
    TBLO

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,758
    Are they located in the fixture and subject to high heat?
    I live for today, I'm just a day behind.

  3. #3
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,620
    Quote Originally Posted by ptonsparky View Post
    I need/want some inline fuse holders, supplementary, that can be used at each 480v fixture.

    Suggestions?
    WE use these for things such as at light pole bases. They come in a number of flavors.
    http://www.cooperindustries.com/cont...ez-series.html

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,758
    Something like texie posted was what I had in mind, but not sure if they will hold up if in fixture with high temps. They probably are most popular one used in pole bases though.
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,619
    Quote Originally Posted by texie View Post
    WE use these for things such as at light pole bases. They come in a number of flavors.
    http://www.cooperindustries.com/cont...ez-series.html
    Yes, those or similar. Being a novice at this one, what does 'breakaway' mean in context with these?
    Tom
    TBLO

  6. #6
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,619
    Quote Originally Posted by kwired View Post
    Something like texie posted was what I had in mind, but not sure if they will hold up if in fixture with high temps. They probably are most popular one used in pole bases though.
    Not in the fixture. More likely in the jbox directly above it. Not sure if that is even legal. in the thinking stage yet.
    Tom
    TBLO

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,758
    Quote Originally Posted by ptonsparky View Post
    Not in the fixture. More likely in the jbox directly above it. Not sure if that is even legal. in the thinking stage yet.
    If a supplemental protector there isn't really any general restrictions on location or ease of accessibility.
    I live for today, I'm just a day behind.

  8. #8
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,053
    Quote Originally Posted by ptonsparky View Post
    Yes, those or similar. Being a novice at this one, what does 'breakaway' mean in context with these?
    I believe the breakaway type is for light poles with breakaway pole bases.
    A breakaway base is designed to breakaway from the pole and concrete base if a vehicle colides with it.
    The breakaway fuse holder would safely disconnect from the load side without leaving a live wire exposed.

    See page 2.
    http://www.cooperindustries.com/cont...s-2130-hez.pdf
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  9. #9
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,837
    Quote Originally Posted by ptonsparky View Post
    Yes, those or similar. Being a novice at this one, what does 'breakaway' mean in context with these?
    Bussman has a lot of options. Our pole bases are called "slip bases" if hit by a car the poles will slip out of the hold down bolts, the breakway fuse holders are intended to disconnect when that happens
    Moderator-Washington State
    Ancora Imparo

  10. #10
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,739
    Quote Originally Posted by tkb View Post
    I believe the breakaway type is for light poles with breakaway pole bases.
    A breakaway base is designed to breakaway from the pole and concrete base if a vehicle colides with it.
    The breakaway fuse holder would safely disconnect from the load side without leaving a live wire exposed.

    See page 2.
    http://www.cooperindustries.com/cont...s-2130-hez.pdf
    More specifically, if the pole is hit, the fuse holder is designed such that the parts come apart and the line side is left electrically dead. It has an extra insulating sleeve inside that stays with the fuse and makes it come out with the load side. So when the pole is hit, the end of the fuse isn't sticking out there like a live "spark plug" waiting for someone to touch it.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...