    Article 110.26, 2008 NEC

    = = >

    Greetings all!

    I am seeking input on some planned new construction......I am
    reviewing plans for a new bldg.......The plans show 4 elec.
    panelboards being installed in one small room.....They are(
    1x) - 400A MDP and (3x) 125A panelboards for lighting, power,
    data, etc.....Two of the 125A panelboards are directly across
    from each other, with the 400A MDP immediately adjacent tot
    hem.

    I am assuming that the MDP will not have a complete cover on
    it, but rather, an inset cover with the circuit breakers accessible.

    My question(s) have to do with the 3 ft. Working Space requirement.
    If I open the panelboard doors on the 2 that are directly across from
    each other, I will not have the 3 ft. minimum to any of these 3 panels
    [ think U-shaped install ].

    Is this an actual violation or violations ?......They have all 4
    panelboards in a room that measures 5 ft. x 6' - 10".

    Thanks for any input !

    < = =

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,385
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If you take the measurements with the panel doors closed do you have the required clearance? If so that's all that you need.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,295
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What voltages are you dealing with?

    Do you have more than one systems in the building with different voltages?
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  4. #4
    Join Date
    Aug 2009
    Location
    inside Area 51
    Posts
    511
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    = = >

    Thanks for the input !

    Regarding the 2 panels directly across from each other,
    ...with the doors closed on both of them, there is approx.4
    .5 ft. between them.......The MDP is approx. 1.5 to the
    left & right of both of these panels.

    These panels are all less than 600v........No other elec.
    systems are involved with these 4 panels.

    < = =

  5. #5
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,295
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Based on 110.26 I do not see an issue with this set up.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  6. #6
    Join Date
    Aug 2009
    Location
    inside Area 51
    Posts
    511
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    = = >

    Much Thanks for the input !

    < = =