    Kitchen "island"
    I have a customer who wants to put a counter top that extends 8" over the counter in an island. I believe the code says that the outlet cannot be over 6" from the edge of the counter. Do I tell them the counter top can't be over 6" over the edge? I don't have my 2014 code book handy now, so I may be misquoting it. Also All counter top outlets must be GFI protected, whether or not they are further than 6ft. from the sink, is this correct? Been a while since I've wired a entire house. Thanks
  2. #2
    Join Date
    Feb 2003
    Somewhere over the rainbow
    Posts
    3,279
    All kitchen receptacles have to be GFCI and AFCI protected.
    As far as the counter issue, just install a receptacle or a power strip under the edge of the counter.
    Edward
    The only thing I know, is the progressive discovery of my ignorance
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,198
    Yes to GFCI protection on all receptacles serving counter tops, for the receptacle to count as the required receptacle the overhang cannot exceed 6". You can still put one there but you will need another to meet the receptacle requirement.
    Rob
  4. #4
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,180
    I would explain the rule to the home owner and see what she/he wants to do
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  5. #5
    Join Date
    Mar 2003
    New York
    Posts
    974
    Mount to the bottom of the overhang.
  6. #6
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,850
    If the overhang is not 8" all the way around, the receptacle can be installed near a corner.
    Quote Originally Posted by sameguy View Post
    Using a Wiremokl box.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor