    Convert 480V current to 208V current

    Hello,

    Is there a specific equation I can use to convert amperage in 480V to 208V? I've been searching the web but can't find a precise formula to use.

    Thanks

  2. #2
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,701
    ?????

    V480 x I480 = V208 x I208
    for constant power
    The difference between genius and stupidity is that genius has its limits.

  3. #3
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,022
    Are you trying to figure transformer primary/ secondary?

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,350
    You could just do a ratio of the 480 volts to 208 volts. For volts 480/208 or 2.3 to 1. For amps 1 to 2.3.

    Ex. 480v and 10 amps = 208v and 23 amps.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by baserunner4 View Post
    Hello,

    Is there a specific equation I can use to convert amperage in 480V to 208V? I've been searching the web but can't find a precise formula to use.

    Thanks
    If they are both single phase or both three phase, you just multiply the current on the primary side by 480 volts, then divide by 208 volts.
    Electricians do it until it Hertz!

  6. #6
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,701
    Quote Originally Posted by baserunner4 View Post
    Hello,

    Is there a specific equation I can use to convert amperage in 480V to 208V? I've been searching the web but can't find a precise formula to use.

    Thanks
    what are you a student of?
    this is one of the most basic principles
    P in = P out for a xfmr (or any device, in this case elec:elec, sometimes elec:mech or the inverse, sometimes thermal:mech, etc)
    P = i x v for 1 ph and sqrt3 x i x v for 3 ph
    The difference between genius and stupidity is that genius has its limits.

  7. #7
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,591
    Quote Originally Posted by baserunner4 View Post
    Hello,

    Is there a specific equation I can use to convert amperage in 480V to 208V? I've been searching the web but can't find a precise formula to use.

    Thanks
    Yes. I @208V = I @480V (480/208)