robert pitre
Member
- Location
- Houma,la
I have a question about bonding?
Upon a inspection I went on was a meter pan and a disconnect panel that was back to back on a wooden 4x6 pole , between the meter pan box and the disconnect box they run sch. 40 pvc.
Looking at the feeder wires they ran 3- 2/0 , 2- hot legs and 1-neutral from the meter pan to the disconnect box.
They also ran a #4 ground wire from the meter pan (only) to a ground rod. This was for a 200amps service with 20amp breaker coming off disconnect box to feed a receptacle with GFIC for a pump to be installed in a pond . My question is this, ( do I need a bonding wire from the meter pan to the disconnect pan )? or ,is the neutral will play the role for the bonding between the meter pan and disconnect box?
Upon a inspection I went on was a meter pan and a disconnect panel that was back to back on a wooden 4x6 pole , between the meter pan box and the disconnect box they run sch. 40 pvc.
Looking at the feeder wires they ran 3- 2/0 , 2- hot legs and 1-neutral from the meter pan to the disconnect box.
They also ran a #4 ground wire from the meter pan (only) to a ground rod. This was for a 200amps service with 20amp breaker coming off disconnect box to feed a receptacle with GFIC for a pump to be installed in a pond . My question is this, ( do I need a bonding wire from the meter pan to the disconnect pan )? or ,is the neutral will play the role for the bonding between the meter pan and disconnect box?