    Quote Originally Posted by Dennis Alwon View Post
    300 x 125%= 380

    The question seems to imply that the breaker is rated 100% but if that is not the case then 400 kcm is correct. The wording, to me, is a bit off.
    Silly me. I thought 300 x 125% was 375.

    Sent from my XT1585 using Tapatalk

  2. #12
    Join Date
    Mar 2018
    Location
    IL USA
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    GoldDigger,

    Electric math doesn't seem to be the same as regular math.

    Click image for larger version. 

Name:	F6-64 (400x640).jpg 
Views:	83 
Size:	33.9 KB 
ID:	20078Click image for larger version. 

Name:	P282 Q52 (640x200).jpg 
Views:	82 
Size:	75.6 KB 
ID:	20079

  3. #13
    Join Date
    Mar 2018
    Location
    IL USA
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Next...
    Click image for larger version. 

Name:	F6-71.jpg 
Views:	85 
Size:	137.1 KB 
ID:	20081
    I understand the neutral sizing starts with 100% continuous load, but how would I know to look to 220.61 and then conclude an unbalanced load of 100A based on what it says?