Thread: Inverter Running at 66% or Transformer

  1. #11
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,209
    Quote Originally Posted by pv_n00b View Post
    From a production point of view it's probably a wash, so look at the relative cost and choose. You can do a simulation of both in SAM but I feel they would come out about the same.
    Inverter efficiencies at different loadings and DC voltages are a bit of a mystery. I have never seen figures on this. You are saying that PV software models this?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #12
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    515
    Yes, PV software that uses the actual equipment in the project does, not PV Watts. SMA has the Sunny Design software that you can use. It's not financial grade but it will show you any difference you can expect and is pretty simple to use.

    Inverter efficiency curves are fairly flat these days across most of the MPPT operating window. They tend to peak at about 80% of full load.

  3. #13
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,209
    Quote Originally Posted by pv_n00b View Post
    Yes, PV software that uses the actual equipment in the project does, not PV Watts. SMA has the Sunny Design software that you can use. It's not financial grade but it will show you any difference you can expect and is pretty simple to use.

    Inverter efficiency curves are fairly flat these days across most of the MPPT operating window. They tend to peak at about 80% of full load.
    Do you know anything off the top of your head about different DC voltages? The fronius primo line of single phase ~240 inverters does 1kv strings, always wondered if you take an efficiency hit for that much bucking.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #14
    Join Date
    Jul 2017
    Location
    Chico, CA, USA
    Posts
    19

    Thanks

    For one project that is 15kw we are opting for a 20kW with a transformer.

    The 21.kW project we are going to use the 30kW. I've used this before on a 19kW system and 11 months later we are still producing what we modeled.

  5. #15
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,277
    Quote Originally Posted by MJRobinson View Post
    For one project that is 15kw we are opting for a 20kW with a transformer.

    The 21.kW project we are going to use the 30kW. I've used this before on a 19kW system and 11 months later we are still producing what we modeled.
    Why would you do that? STC conditions rarely if ever exist in the real world. We routinely design and build PV systems with DC:AC ratios of up to 1.2 and they are all monitored. In nearly three years with this company with hundreds of systems I have seen very minor clipping only once or twice. The rest don't clip - ever.

  6. #16
    Join Date
    Jul 2017
    Location
    Chico, CA, USA
    Posts
    19

    Sizing answer

    Quote Originally Posted by ggunn View Post
    Why would you do that? STC conditions rarely if ever exist in the real world. We routinely design and build PV systems with DC:AC ratios of up to 1.2 and they are all monitored. In nearly three years with this company with hundreds of systems I have seen very minor clipping only once or twice. The rest don't clip - ever.
    We had a SMA20 in stock gathering dust to use with the 15kW system.

    The 21kW system we used the SMA30 because of cost of SMA20 + Transformer + Additional Disconnects.

    Thanks

  7. #17
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,303
    Quote Originally Posted by electrofelon View Post
    To elaborate on what JB said, dont just think of the transformer cost, but also the labor and balance of system components. If it's not an auto, you need a GEC which can be a hassle for a rooftop system. We had to do a bunch of transformers on a rooftop system and it was super time consuming.
    How is the external transformer's topology relevant to whether or not a GEC is needed for the PV array on a rooftop? I thought that depends on whether or not there is a transformer in the inverter, rather than an AC-side transformer on the system.

    I know GEC's in general are needed for any isolating transformer, but I didn't think that would mean the GEC is required to extend all the way to the PV array.

  8. #18
    Join Date
    May 2011
    Posts
    4,122
    Quote Originally Posted by Carultch View Post
    How is the external transformer's topology relevant to whether or not a GEC is needed for the PV array on a rooftop? I thought that depends on whether or not there is a transformer in the inverter, rather than an AC-side transformer on the system.

    I know GEC's in general are needed for any isolating transformer, but I didn't think that would mean the GEC is required to extend all the way to the PV array.
    Maybe if your using the roof for the transformer equipment because there aren't better locations. I can how see a 'CAD monkey' designer with no installation experience might think that's a great idea when it isn't. I think the point is, take the details into consideration. A transformer has to save more money than the cost of the transformer.

  9. #19
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    515
    Quote Originally Posted by electrofelon View Post
    Do you know anything off the top of your head about different DC voltages? The fronius primo line of single phase ~240 inverters does 1kv strings, always wondered if you take an efficiency hit for that much bucking.
    The general rule of thumb is that there is little penalty for bucking and a more significant penalty for boosting. Equipment manufacturers try to avoid boosting if possible and as string voltages go up the need for boosting has gone down. A 480Vac system needs an MPPT voltage of more than 480*√2 = ±679Vdc to avoid a boost circuit, a 277V WYE needs ±392Vdc and a 240Vac system needs ±340Vdc. Just ballpark figures but it gives an idea.

  10. #20
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,209
    Quote Originally Posted by Carultch View Post
    How is the external transformer's topology relevant to whether or not a GEC is needed for the PV array on a rooftop? I thought that depends on whether or not there is a transformer in the inverter, rather than an AC-side transformer on the system.

    I know GEC's in general are needed for any isolating transformer, but I didn't think that would mean the GEC is required to extend all the way to the PV array.
    I was thinking of the case where the transformers are on the roof, thus you would need to get a GEC down to the building GES or building steel. On the other hand, an isolating transformer will have taps which may be handy.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"