not in my opinion.

An assembly occupancy usually has a higher number of people per unit area. Think areas like stadium seating at a sports venue, or seating at a church or theater, or a crowded nightclub.

In a fitness center, people and equipment usually require too much space for it to be an assembly occupancy.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
After reading the intro to NEC 518, I think it depends on the area.

The NEC handbook has a table extracted from NFPA 101. For a gym with equipment, occupancy is calculated based on 50 SF per person. For a gym without equipment, its based on 15 SF per person.

So if you have a room with equipment and its over 5000 SF, that means your occupancy would be over 100 people, and it would be an assembly. If you have a room and no equipment, 1500 SF would be the limit, and anything larger would be an assembly occupancy.
 

jfiorini

Member
Location
vermont
guess ill have to fid out what the square footage is... I don't see a plaque stating the Max occupancy... I am certain that it is less than 5000sq feet
 