User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 17
Thread: Exam Question
  1. #1
    Join Date
    Dec 2017
    Buckhannon wv USA
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Exam Question
    I hope some can help?My question is From my exam I took and got it wrong .Determine the minimum required conductor ampacity for an induction type motor 25 HP 460 volts 3 phase squirrel cage motor name plate full load 32 amp service factor 1.15?My answer was 34x1.25 =42.5A there answer was 43 A .The only thing I can figure is they rounded up.Any help would be greatly appreciated
  2. #2
    Join Date
    Oct 2015
    US
    Posts
    798
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    42.5a is not a standard breaker size , though neither is 43 .45 would be the best answer inmo as you can round up for branch ckts but not for feeders
    Sent from my SM-G950U using Tapatalk
  3. #3
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hmm, doing the math off of that question, I would have gotten 40 amps (nameplate FLA x 1.25). Not sure what the annex of the NEC has to say about it.
    Nickelec, the breaker can be up to 250 percent of the FLA. The motor could very well have a 60 amp breaker with #10 THHN
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,639
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The question is about sizing the conductor so forget about the OCPD. You need to also ignore the nameplate current and find the appropriate value in T430.250 (as you did) and use that for the calculation. For rounding up or down (B) applies.
    220.5 Calculations.
    (A) Voltages. Unless other voltages are specified, for purposes of calculating branch-circuit and feeder loads, nominal system voltages of 120, 120/240, 208Y/120, 240, 347,480Y/277, 480, 600Y/347, and 600 volts shall be used.
    (B) Fractions of an Ampere. Calculations shall be permitted to be rounded to the nearest whole ampere, with decimal fractions smaller than 0.5 dropped.
    Rob
  5. #5
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,331
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dsm View Post
    Determine the minimum required conductor ampacity . . . .
    As Rob pointed out, this question is not about the breaker. It is also not about sizing the conductor. It is about determining a specific number. I think your method is right, and the exam author's answer is wrong.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,639
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    Wouldn't 42.5 be rounded up to 43 which is the answer given?
    Rob
  7. #7
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    43 amps is correct you round down fractions smaller than .5.
    That said, I don't know why using the name plate is incorrect.
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I didn't check the calculations, but if he did calculations correctly and came up with 42.5, then IMO 42.5 and 43 are both correct answers.
    It says right in the section you quoted that you are permitted to round this up - not that you shall round it up.
    I live for today, I'm just a day behind.
  9. #9
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    I would assume that the nameplate figure of 32A is correct for that particular motor assuming it is a real motor.
    Making typical assumptions for effy and pf that's about what I come up with.
    However, the tables probably have to be conservative.
  10. #10
    Join Date
    Dec 2010
    Posts
    69
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I thought ampacity of conductors was determined by the table values, not the nameplate.