    Emergency lights

    Do I need to run two separate conduits for the emergency lights on a battery backup inverter??

  2. #2
    Join Date
    Nov 2014
    Location
    Parker CO
    Posts
    13
    300.3(C)1 says conductors of AC and DC circuits rated 1000V or less shall be permitted to occupy the same enclosure, cable or raceway. An old company I was at had stickers to add on conduit if they contained wiring fed from 2 dif. systems, to help out the next guy who came along

  3. #3
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    401
    Quote Originally Posted by B4097 View Post
    Do I need to run two separate conduits for the emergency lights on a battery backup inverter??

    Are you supplying lights with a normal circuit and an emergency circuit?