Results 1 to 5 of 5
Thread: Electrician
  1. #1
    Join Date
    Apr 2009
    Posts
    2
    When meggering power panels, denergized and all breakers off, do you have to disconnect the newtral from the secondary of Y transformer panel to megger the leads to the power panel?
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,543
    Quote Originally Posted by yucatan4 View Post
    To test the ungrounded conductors you shoudn't have to. If you were to test the neutral - you would have to disconnect it or any bonding jumpers in the system.
    I live for today, I'm just a day behind.
  3. #3
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,822
    When checking the phases from the transformer to the panel, yes, isolate the neutral or else remove the conductors from the transformer.
    We usually isolate all of the conductors.
    Tom
    TBLO
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,543
    Quote Originally Posted by kwired View Post
    To clarify if the ungrounded conductors are still connected to the transformer (directly or via closed switches) you will read through transformer windings as well as system bonding jumpers and not get results you are wanting.
    When megging or continuity testing you must eliminate unwanted paths that can effect the readings.
  5. #5
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,363
    . .can affect...
Posting Permissions
  • You may not post replies
  • You may not edit your posts
