    On a indoor hot tub installed in doors must I use a insulated EGC ?

  2. #2
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,364
    IMHO ..Without more detail and if it's a genuine hot tub, yes...

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,856
    If it is residential install then you can use nm cable for the tub indoor. The only issue is if the manufacturer requires a full size equipment grounding conductor.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,364
    I had a guy install a full size outdoor type hot tub indoors and right in the middle of a small living room. You had like 4ft to walk around it to get to the front door. It was the craziest thing.

    Yes... but to the OP . Is it in a hotel ?

  5. #5
    Join Date
    Feb 2004
    Posts
    625
    Quote Originally Posted by Dennis Alwon View Post
    If it is residential install then you can use nm cable for the tub indoor. The only issue is if the manufacturer requires a full size equipment grounding conductor.
    It is in side ( residential ) any code reference PLEASE ?

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    35,680
    Quote Originally Posted by domnic View Post
    It is in side ( residential ) any code reference PLEASE ?
    try looking at 680.21 for the non insulated EGC in NM cable.

    110.3(B) for when instructions require full sized EGC.
    I live for today, I'm just a day behind.

  7. #7
    Join Date
    Feb 2004
    Posts
    625
    Quote Originally Posted by kwired View Post
    try looking at 680.21 for the non insulated EGC in NM cable.

    110.3(B) for when instructions require full sized EGC.
    680-21-4 THANK YOU. no insulated egc required on inside residential hot tub. when using nm cable with egc in the cable.

  8. #8
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,856
    680.43 is the appropriate article as it states chapter 3 wiring methods