Thread: 200 Amp residential service

  1. #21
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,657
    Quote Originally Posted by infinity View Post
    I agree and admit that the LB is easier to install for that reason and looks better when finished. There is always a chance with the LB that an inspector could make you change it.
    Just an FYI, it was done that way originally and passed inspection. That doesn't necessarily make it right though. I don't know how it passed on the original installation based on how poorly it was installed. When I got to the job the first day the service was hanging on by a thread. The meter pan wasn't even attached to the house. The sheathing under the siding was dry-rotted. AND, that was only done 3 years ago.

  2. #22
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,157
    Quote Originally Posted by romex jockey View Post
    On the driveway physical protection , why can't a few pillars be installed for 'vehicular' safety?

    ~RJ~
    The cost to do that justifies using RMC in the first place, though the bollards would protect more then just the raceway.

    Quote Originally Posted by goldstar View Post
    Dennis, I checked with an EI (who is also one of our CEU instructors and on the licensing board for the State) and he advised me that on a single family residence the norm is to drop down 2 sizes on a service.(at least that's here in NJ). If you look at SEU cable that's the way it's constructed. Shouldn't make any difference if you're using single CU or AL conductors.

    I started this thread because I generally use SEU cable and haven't installed a 200A service using PVC and single conductors in a long time. I wanted to check with some of my colleagues on wire sizes before placing an order. I was surprised to find out how many didn't know about 310.15(B)(7) and down-sizing the wire. After hearing their answers I started thinking "Maybe there was something I missed".
    NEC only says the neutral needs to be able to handle the load it will carry, but never can be smaller then the required grounding electrode conductor. There are jurisdictions that won't question the load as long as you don't go less then two sizes smaller then the ungrounded conductors.
    I live for today, I'm just a day behind.

  3. #23
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,657
    Quote Originally Posted by kwired View Post
    The cost to do that justifies using RMC in the first place, though the bollards would protect more then just the raceway.
    Granted, but it's not going to protect me from my wife who wouldn't want an ugly bollard in the driveway. Houses in the area where this installation is are fairly close together. Taking up a foot or so of the driveway at the service location could present a problem for the HO.

  4. #24
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,631
    Quote Originally Posted by infinity View Post
    ...I agree, but I seem to remember hearing about the two size reduction too.
    That was last in Note 3 in the "Notes to Ampacity Tables of 0 to 2000 Volts" in the 1993 code. The note was changed to eliminate the specific permission for the the neutral to be two sizes smaller in the 1996 code.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  5. #25
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,631
    The change was the result if a proposal submitted by Charlie Trout with the following substantiation:
    SUBSTANTIATION: The NEC provides adequate requirements for the sizing of the grounded conductor. Note 3 correctly requires compliance with Sections 215-2, 220-22, and 230-42. The additional restriction of being permitted to be not more than two AWG sizes smaller than the ungrounded conductors has no relevance to grounded conductor sizing. Using Note 3 as presently written requires a larger grounded conductor than not using Note 3.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  6. #26
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,657
    Thanks for doing that research Don.

  7. #27
    Join Date
    Apr 2009
    Posts
    210
    I've always found that 2 1/2" is better all around for the 200a entrances when negotiating turns and radius changes etc. My 2 cent.
    Also I believe the POCO here which is National Grid, specs that it be in 2.5" conduit for a riser, I know this isnt a riser just sayin.

  8. #28
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,333
    I have never seen anyone run 2 1/2" conduit for a dwelling service. I have seen LB's increased in size for se cable.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  9. #29
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,631
    Quote Originally Posted by newservice View Post
    I've always found that 2 1/2" is better all around for the 200a entrances when negotiating turns and radius changes etc. My 2 cent.
    Also I believe the POCO here which is National Grid, specs that it be in 2.5" conduit for a riser, I know this isnt a riser just sayin.
    Utility riser conduit specs are typically based on the mechanical strength required to support their service drop.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  10. #30
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,333
    I always considered the riser as the conduit or cable from the meter to the point of attachment on the building. The mast was the conduit- 2"rmc around here, that went thru the roof and supported the service drop. 230.28 seems to support the mast statement.