    The situation I 've been asked about is --- the pool deck will have drains for shed water, the pool drain piping is to be a PVC material, the contractor has been asked to install an 240v deicing heat cable in the piping, & now the NEC does not require circuits to be pool associated outside of 5'of waters edge.
    I really can't justify 680.27(C)(3) as the cables do not meet the embedded requirement/or do they?
    Violation? Hazard?? or just wrong???
    680.27 Specialized Pool Equipment.
    (C) Deck Area Heating. The provisions of this section shall apply to all pool deck areas, including a covered pool, where electrically operated comfort heating units are installed within 6.0 m (20 ft) of the inside wall of the pool.
    (3) Radiant Heating Cables Not Permitted. Radiant heating cables embedded in or below the deck shall not be permitted.
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  2. #2
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,876
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mwm1752 View Post
    [B]Violation? Hazard?? or just wrong???.
    You are right it's not a violation because the cables are not embedded.
    Maybe a hazard, but that depends how easy it is for someone to come into contact with the heat cables and other parts of the electrical installation.
    Just wrong? That's the big question. What if, instead of around a pool in pvc, the heat tape was installed in a metal gutter and downspout at an elementary school or daycare? At least around the pool you have a bonding grid.
    If you don't think too good, don't think too much.
  3. #3
    Join Date
    Feb 2007
    USA
    Posts
    5,805
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    It is still a violation if it is below.
    "Radiant heating cables embedded in or below the deck shall not be permitted."
  4. #4
    Join Date
    Feb 2009
    Posts
    9,876
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    I don't think you know what embedded means.
  5. #5
    Join Date
    Feb 2007
    USA
    Posts
    5,805
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I do , do you?
  6. #6
    Join Date
    Oct 2015
    US
    Posts
    789
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    What's the heat cables purpose? If its purpose is to keep the pipes from freezing I wouldn't really call it radiant heating cable
    Sent from my SM-G950U using Tapatalk
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I do , do you?
    Op says heat cable is in the piping.
    I would assume this means it can be pulled out and repaired or replaced if necessary without the need to destroy the decking.
    I live for today, I'm just a day behind.
  8. #8
    Join Date
    Feb 2007
    USA
    Posts
    5,805
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I don't think the issue of accessible to repair is the issue. Anyone know what the CMP thought on this one?
  9. #9
    Join Date
    Feb 2009
    Posts
    9,876
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There is electric heat tape that gets embedded in the concrete, we call it snow melt around here. I don't know for sure, but I bet that's the stuff they want to keep out of concrete surrounding pools.
  10. #10
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,128
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    As I read the code section I say it is not compliant to have the heating cable below the deck even if it is in pvc conduit. I am not sure that is the intent however if the cable should fail and leak to ground- assuming it can just as water can usually get inside the conduit, then there is a potential for an accident.