Results 1 to 8 of 8
Thread: SPLICING PARALLEL 3/0 TO SINGLE 500 MCM
  1. #1
    Join Date
    Apr 2006
    Upstate S.C.
    Posts
    845
    Working on the design for an existing facility. Need to splice existing parallel 3/0 per phase to existing single 500 MCM per phase.
    Any suggestions?
    Thanks,
    RC
    It's my name going on that drawing, not yours. If what you want ain't right, it ain't going on the drawings!
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    A Polaris connector is what you want, available at a supply house or Big Box store for about $40 a piece
    Electricians do it until it Hertz!
  3. #3
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,672
    As mentioned, any decent supply house will stock the most common ones. I think stock at a big box store would be iffy though. Take a look here: https://polarisconnectors.com/index.html
  4. #4
    Join Date
    Apr 2006
    Upstate S.C.
    Posts
    845
    Thanks. I will use the 3 port with the 500 MCM in the middle port and the 3/0's on either side.
    RC
  5. #5
    Join Date
    Jul 2013
    Renton, WA
    Posts
    851
    Yep, simpler than cadweld for your application if normal power.
    Last time I spliced a few 4/0 to bigger stuff ended up doing cadweld, but was dealing with 250kA pulse tester at military site discharging a semitruck load of HV capacitors into service (poco disconnected obviously) to test a power system for EMP.
    Any connectors tried would arc and the cables would pull out of connectors due to magnetic forces.
  6. #6
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,551
    Insulated taps or distribution blocks are our usual methods.
  7. #7
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    1,809
    Quote Originally Posted by junkhound View Post
    ..dealing with 250kA pulse tester.. Any connectors tried would arc and the cables would pull out of connectors due to magnetic forces.
    Similar amperage to lighting strikes.
    The peak temperatures within a lightning channel are known to exceed 30,000 K, with sufficient pressure to produce planar deformation features, PDFs are only produced by extreme shock compressions on the scale of meteor impacts.
    See Fulgurites https://en.wikipedia.org/wiki/Fulgurite
    Roger Ramjet NoFixNoPay
  8. #8
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    I've seen YouTube videos of Manufacturers testing fault currents in that range for cable clamping systems. it was pretty scary to see those cables come out of insufficient clamps and whip around with enough Force to easily kill somebody, just from the impact, no electrocution involved.