Originally Posted by
zbang
With cord drops, you need proper strain-reliefs at the top and bottom and you can't use a handy-box for the receptacle (none of this is in Art 400). You'll find more discussion of this sort of thing by searching the forums.) You might also run into the prohibition of using flex cord in place of fixed wiring.
Because the columns are only 20-30' apart, you could put a quad on each one and call it done.
If cost permits, make each location it's own circuit; it'll help prevent one artist's heater from tripping off another artist's work lights.
First item mentioned in 400.7 uses permitted is pendants.
You are correct on not using a handy box - it must be a box rated for pendant use.
If only a single receptacle is desired a basic cord connector is fine at the end.
I live for today, I'm just a day behind.