    Quote Originally Posted by electrofelon View Post
    A lockout is a few bucks - no "special breaker" required, and then it doesn't have to be within sight.
    Lock-Out-Tag-Out devices are not acceptable, they can be removed, leaving occupants with no means to lock.

    You might put a lock on the fuse box door.

    There is also an exception, referencing 422.34 for Unit switches with an "Off" position. Stop/Reset doesn't count.
    Last edited by ramsy; 04-16-18 at 04:45 PM.
    Roger Ramjet NoFixNoPay

  2. #22
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,624
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    A lockout is a few bucks - no "special breaker" required, and then it doesn't have to be within sight.
    Quote Originally Posted by ramsy View Post
    Lock-Out-Tag-Out devices are not acceptable, they can be removed, leaving occupants with no means to lock.

    You might put a lock on the fuse box door.
    I believe that Ethan was referring to a 110.25 breaker locking device, not a temporary lock out tag out device.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #23
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I believe that Ethan was referring to a 110.25 breaker locking device, not a temporary lock out tag out device.
    Yes something like this right? I believe this is acceptable no?

    https://m.lowes.com/pd/Square-D-Load...-Locks/3459910
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #24
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,624
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    That would work.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #25
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Yes something like this right? I believe this is acceptable no?

    https://m.lowes.com/pd/Square-D-Load...-Locks/3459910
    In store pickup is not available for this product. Inspector can red-tag until item is shipped & installed.

    Better to hire those who install the cord & plug disconnect.
    Roger Ramjet NoFixNoPay

  6. #26
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,808
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ramsy View Post
    Santa Ana, CA senior planner, and Education Chair for Orange Empire Division IAEI, provides the mandatory continuing-education units for several municipal-inspection departments. He is one of the best, and cities send their inspectors from all over the Los Angles basin.

    http://www.iaei.org/web/orangeempire
    As of 4/16/18 the education notes for NEC Art. 422 are still published on home page.

    The monthly meetings are attended by ~50 people, combination inspectors, contractors, Utility, NRTL, & OSHA reps. I've been an attending member for ~10 years.
    Thanks being involved.
    I don't see this on the link you provided.

    Can you post the direct link.

  7. #27
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No other link. IAEI meetings are open to the public.
    Orange Empire includes a buffet lunch - $25 Non Members
    Roger Ramjet NoFixNoPay

  8. #28
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,808
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ramsy View Post
    No other link. IAEI meetings are open to the public.
    Orange Empire includes a buffet lunch - $25 Non Members
    You say the info is on the home page.

    As of 4/16/18 the education notes for NEC Art. 422 are still published on home page.

    I don't see it. Where is it , can you provide some more info, a screenshot?

  9. #29
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    I don't see it. Where is it?
    Scroll down for education, its just a topic introduction for most recent month.

    You need to attend for the Full Monty
    Roger Ramjet NoFixNoPay

  10. #30
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,808
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ramsy View Post
    Scroll down for education, its just a topic introduction for most recent month.

    You need to attend for the Full Monty
    why post something that we cannot see unless a member.
    Geez.