Results 1 to 4 of 4

Thread: ground loop test and earth resistance test

  1. #1
    Join Date
    Dec 2005
    Posts
    113

    ground loop test and earth resistance test

    Good day,
    Can anyone explain the difference between these tests and how they are done?
    Last edited by GoldDigger; 04-15-18 at 07:34 AM. Reason: Speling in title

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,437
    Is there anyone that has any idea to help this member
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,779
    Ground loop test is typically done with a clamp on ground tester, of course there are many stipulations on this test that has been discussed dozens of times in detail here.

    Earth resistance is typically done with a 3 point fall of potential test and is much more reliable because the test proofs itself as being accurate, again discussed many times here in detail.

  4. #4
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    this may help
    basically stated above
    earth resistance measures the coupling of your gnd system with earth reference
    ground loop similar but used for measuring effectiveness of equip bonds
    measures a loop between existing electrodes


    earth resistance testing https://assets.tequipment.net/assets...ownToEarth.pdf