    Service conductor length before needing a disconnect.

    Thursday April 12th I removed and replaced an old fuse box service. Because of the width of the new 100 amp 32 space panel I had to move it around the corner. So the SEC comes into the house and is infused for 22" between meter and panel. The inspector is calling for a disconnect to be installed. Amy arguments i could make? I mean it is less distance than a Sweep 90. or would I need to sleeve it in something. I was always told 3 feet of service cable into the house before needing a disconnect and have had other inspectors say 6 feet. Any input would be appreciated.
    Attached Images Attached Images  

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,724
    Code says "nearest the point of entrance" (230.70) so you are pretty much regulated by that Code jurisdiction's interpretation. You might ask if installing the conductors in a metallic wireway would make any difference. Often with that protection, a longer length is accepted.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,851
    If that is a service cable then why does it have 4 conductors? Looks like SER not SEU.

    If they are service conductors then I would agree with the inspector. Some areas have amendments that actually state the length of wire while others just use the somewhat ambiguous nec RULE.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,466
    Pretty much up to the AHJ. Around here it's 5 feet but that's usually running exposed in a basement. The fact that yours is buried in the wall is probably the reason for the concern. Since you already have SER it should be an easy change.

    -Hal

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    24,724
    As mentioned it's a judgement call but I would probably allow it. I wouldn't allow the four conductor cable to be used as shown in the photo. You have a choice, either add the disconnect on the outside or change to a raceway and encase it in concrete.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Sep 2011
    Location
    woodbridge, ct. USA
    Posts
    1,060
    Quote Originally Posted by petchman5 View Post
    Thursday April 12th I removed and replaced an old fuse box service. Because of the width of the new 100 amp 32 space panel I had to move it around the corner. So the SEC comes into the house and is infused for 22" between meter and panel. The inspector is calling for a disconnect to be installed. Amy arguments i could make? I mean it is less distance than a Sweep 90. or would I need to sleeve it in something. I was always told 3 feet of service cable into the house before needing a disconnect and have had other inspectors say 6 feet. Any input would be appreciated.
    Since it is only 100 amp you can get a small panel to use as a disco. GE makes a 4ckt panel rated 125 amp for less then $30. It comes with a small square washer to use as a lock down, so the main is ok. Of course you will have to buy a 100 amp breaker also.

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    35,668
    5 feet of conductor inside the building is the rule here. There are times when they might allow a little more - you better ask first though in those situations.

    Only thing wrong with using 4 wire cable like OP did is he essentially has a parallel neutral, assuming N and G are both connected in the meter. Disconnect the bare conductor (at least on one end) and nothing wrong with it. Still leaves a grounded "shield" if only connected at one end and shoulnd't be anything wrong with that.
    I live for today, I'm just a day behind.

  8. #8
    Join Date
    Apr 2005
    Location
    Atlanta,GA
    Posts
    5,712
    Quote Originally Posted by Dennis Alwon View Post
    If that is a service cable then why does it have 4 conductors? Looks like SER not SEU.

    If they are service conductors then I would agree with the inspector.
    Dennis you have good eyes, I didn't even notice that.
    The 95% of people that you can't trust give the other 5% a bad name.

  9. #9
    Join Date
    Nov 2007
    Posts
    869
    It would be nice to have a specified length written in the code for distance into a building.

    This has always been a crapshoot when it comes to what is allowable.Why for instance can't there simply be a length, period, end of discussion.

    A number of times I have installed a disco only to have the inspector say" you were fine with the length, you didn't need that switch outside.

    When working in a variety of municipalities, it's not practical call every inspector and ask what they will allow,

    2'
    3'
    4'
    Etc.

    Pick a number and that's that.

  10. #10
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,865
    Washington state code explicitly states that the limit here is 15 feet. I don't know if MN has a similar code. Have you looked for applicable state codes?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •