    Changing a panel that has a Trane 10 ton 2 stage package 3 phase (NO heat) a/c connected. Plate is worn so I can't read the Maximum breaker requirement.
    Anyone have experience with these? Need to install the correct breaker.
    thx
  2. #2
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What was there before. That would be my first thought.
    Tom
    TBLO
  3. #3
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The 10-ton 3-phase, 208 volt units at the hotel we're supposed to be on 100 amp Breakers. I found all three units wired into a 250 amp breaker, with the wires having a massive haircut so they'd fit in the terminals.
    A call to train, or a Google search about model should reveal the MOCP.
  4. #4
    Join Date
    Mar 2003
    New England
    Posts
    13,683
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can you still read the compressor and condenser fan motor labels? That's where I would start and then do the math from there.
  5. #5
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    mca 49
    max cb 60
    187-253 vac
    call trane
    rating is voltage dependent
    the unit voltage is an important detail
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ingenieur View Post
    mca 49
    max cb 60
    187-253 vac
    call trane
    Age of unit and SEER rating can have some impact,
    10 tons is good starting point information to some extent though.
    OP does this have multiple compressors or a single compressor? I can easily see it being a two compressor unit. 2 stage could easily be each compressor is one stage.
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Mar 2003
    New England
    Posts
    13,683
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Scroll, recip or semi-hermetic compressor will also make a difference.
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by peter d View Post
    Kind of one of those things that makes for different SEER ratings over the years.
  9. #9
    Join Date
    Mar 2003
    New England
    Posts
    13,683
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Yes, anything older will likely be a semi-hermetic in these tonnages. These days practically everything is scroll. I suppose units can still be custom made with with semi-hermetics but why?
  10. #10
    Join Date
    Aug 2016
    fl
    Posts
    94
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Unfortunately unqualified persons have been working on this site, I have to do my due diligence and find out for myself. I am not comfortable with what was there before. Already found a 12 awg ground wire for the entire 200a panel. had to fix that.