    ABOVE CEILING DISCONNECT FOR VAV BOXES

    I used to spec BUSSMANN SSU5 for this but I can't find them in the Bussmann site.

    What do you use to serve as a small 120V fused disconnect for VAV's? The VAV's we are using con'tr have a fan, only a small 30VA transformer integral with the VAV. We plan on feeding 5 - `10 VAV's off a single 20A circuit.

    Thanks.

    RC
    Last edited by Ragin Cajun; 04-16-18 at 01:31 PM.
    It's my name going on that drawing, not yours. If what you want ain't right, it ain't going on the drawings!

  2. #2
    Join Date
    Jan 2014
    Location
    chicago, il, USA
    Posts
    414
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You could put a single 120/24vac power supply near the electrical panel and then feed 24 volts to each of the VAVs. We install 24/24 isolation Transformers in each VAV with a single fuse on the primary side of the Transformer. This fuse is really used more like a disconnect since most Transformers less than 50 VA have inherent protection. It does provide protection as well, it's just not really required.
    The world is round, you will get there no matter what path you take.

  3. #3
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,854
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ragin Cajun View Post
    I used to spec BUSSMANN SSU5 for this but I can't find them in the Bussmann site.

    What do you use to serve as a small 120V fused disconnect for VAV's? The VAV's we are using con'tr have a fan, only a small 30VA transformer integral with the VAV. We plan on feeding 5 - `10 VAV's off a single 20A circuit.

    Thanks.

    RC
    Why do you feel you need a fused disconnect? Or is it just preference? We use a standard 20A 1221 Hubbell switch all the time.


    I know what I don't know, and I know where to go to find it!

  4. #4
    Join Date
    Jan 2018
    Location
    SE Michigan
    Posts
    120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ragin Cajun View Post
    I used to spec BUSSMANN SSU5 for this but I can't find them in the Bussmann site.
    RC
    Still has the same Cat # SSU

    http://www.cooperindustries.com/cont...plugfuses.html

    MTW

  5. #5
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,928
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Okay, nobody has ever accused me of being shy, so I'll ask: What the heck is a VAV?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  6. #6
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,232
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Okay, nobody has ever accused me of being shy, so I'll ask: What the heck is a VAV?
    VAV stands for Variable Air Volume as a general concept in HVAC, where the system supplies air into ducts at a constant temperature, and the temperature in individual rooms is controlled by letting in (and exchanging) more or less of that air. A VAV box is a motorized damper that makes that happen. What he is talking about is the way power is delivered to that VAV box, which is usually 120V (sometimes 277V) that then goes to a plug-in power supply that powers a 24V little reversing gear motor that moves the vanes inside the duct. The motors are actually cool little units, I have used the cheaper simpler ones (without all the direct digital control stuff) for other high torque-low speed needs.

    Here's a somewhat simple one, they can get a lot more complex than this though.
    Click image for larger version. 

Name:	c9ed2b03-2e22-4678-bf40-e636cca25624.jpg 
Views:	38 
Size:	17.4 KB 
ID:	20167

    Motor
    Click image for larger version. 

Name:	vav motor.jpg 
Views:	39 
Size:	8.3 KB 
ID:	20168
    Last edited by Jraef; 04-17-18 at 12:14 AM.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  7. #7
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,928
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ah, a motorized damper.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  8. #8
    Join Date
    Apr 2003
    Location
    Planet macmikeman
    Posts
    3,487
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I just use a single pole 20 amp rated switch. The only reason I use a 20 amp one is specs. A .35 cent hardware store 15 amp 120 volt switch would work fine in the same application, but spec is spec.
    85deg. an Sunny today.

  9. #9
    Join Date
    Dec 2008
    Posts
    535
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There are 2 types of VAV boxes in my buildings, one is a series unit, fed w/24v., only power needed is for the damper motor. The other is called a parallel box, these units have the same 24v. damper motor, but fed with 277v., which powers the reheat (duct heater) and a fan, which operates on heat only, with a separate non-powered damper.
    Mt. Falls, Va.
    "Not a sermon, just a thought"
    A licensed electrically-related individual

  10. #10
    Join Date
    Jul 2013
    Location
    Moab, UT USA
    Posts
    249
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    VAV Specifics

    Quote Originally Posted by macmikeman View Post
    I just use a single pole 20 amp rated switch. The only reason I use a 20 amp one is specs. A .35 cent hardware store 15 amp 120 volt switch would work fine in the same application, but spec is spec.
    I would also ask why the fused disconnect is needed.
    I have worked on all manner of VAV boxes, also depending on the configuration known as Fan Powered Boxes. IN these cases I would assume the disconnect has to be motor rated. I detest fuses on fan drive gear, but its often seen on the electric heat side.
    They come in all types of configurations. I have seen 115V-1, 240V-1, 240V-3,277V-1, 480V-1 etc.
    The FPBs will mostly have fan drive motors of the typical squirrel cage type.
    The dampers are historically pneumatically controlled but with DDC there is everything anymore.
    In Exterior zones in Multi-Story they can contain resistance heat packs.