    Underground Temp Cable

    I have to temp out an existing service. So I'm running from utility property line box to new box where I intercept existing incoming conductors. Going tyo need a few sets of #500. Can I use USE cable as direct bury? If not guess PVC I the way to go? Thanks
    Attached Images Attached Images  

  2. #2
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,438
    You can direct bury USE cable. You're going to need more than what I would consider a hand hole box to splice them, and maintain proper bending radius.

    Anyone who has moved a service like this, I would be interested in learning how exactly this is accomplished... I've never seen rmc threaded once it's already in the ground, or with wire in it. Does one cut the existing service ~ 5 ft closer to the utility, then cut roughly five foot of conduit off to have working length with the existing conductors? Or is the whole thing repulled as one solid run? How big of a trench would this typically require for the above posters scenario
    Electricians do it until it Hertz!

  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,750
    Quote Originally Posted by JFletcher View Post
    Does one cut the existing service ~ 5 ft closer to the utility, then cut roughly five foot of conduit off to have working length with the existing conductors?
    I've never done it either but I would do as you describe. Question is what happens when the temporary isn't needed anymore? Looks to me like the whole UG run will need to be replaced.

    -Hal

  4. #4
    Join Date
    Jul 2015
    Location
    Soldotna, AK, USA
    Posts
    124
    Quote Originally Posted by JFletcher View Post
    You can direct bury USE cable. You're going to need more than what I would consider a hand hole box to splice them, and maintain proper bending radius.

    Anyone who has moved a service like this, I would be interested in learning how exactly this is accomplished... I've never seen rmc threaded once it's already in the ground, or with wire in it. Does one cut the existing service ~ 5 ft closer to the utility, then cut roughly five foot of conduit off to have working length with the existing conductors? Or is the whole thing repulled as one solid run? How big of a trench would this typically require for the above posters scenario
    This is a good sized task and could be done a bunch of ways really.

    If I was asked to do it, I would look at removing conductors first. Not only for possible reuse on load side, but I think it will make conduit work quicker and digging footprint smaller IMO.

    I would hide the existing empty service conduits stubbed up in a appropriate vault.