User Tag List
Results 1 to 5 of 5
Thread: Sizing a Utility Transformer for PV and Building Load
  1. #1
    Join Date
    Dec 2017
    CA
    Posts
    13
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello,
    Say I have a 2 building loads of 208Y/120A at 400amps. The transformer cans are 3 50KVA at 208Y/120V. I want to interconnect at the splice blocks the secondary side of the transformer so it will offset both mains and their respective meters. I'll be using inverters that have a 40A max. Can I size up to 320A or 400A for the solar? Is there anything else that I should be careful of? I will be seeking out to a professional just trying to get a heads up before I approach them.
    Thanks
  2. #2
    Join Date
    May 2011
    Posts
    4,877
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by baserunner4 View Post
    Hello,
    ... I want to interconnect at the splice blocks the secondary side of the transformer so it will offset both mains and their respective meters. ...
    What does that mean? Where are the meters? You cannot backfeed two meters with one solar system. What is the metering regime for this solar system?
    Other than that, if you have a supply side connection and a 400A service then you could backfeed 320A nameplate inverter current, yes.
  3. #3
    Join Date
    Dec 2017
    CA
    Posts
    13
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I didn’t think of that. I think it would be a new service. The current meters are after the main circuit breakers.
  4. #4
    Join Date
    Nov 2015
    CA, USA
    Posts
    717
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello,
    Thanks
    400A OCPD and 320A inverter output. NEC 705.12(A), "The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service." The utility will have to allow virtual net metering for this to offset the meters.
  5. #5
    Join Date
    Nov 2015
    CA, USA
    Posts
    717
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I should say one more thing on this subject. Utilities rate things differently then we do based on the NEC. So while the distribution transformer might have a nameplate rating of 150kVA and the utility owned conductors might be rated for 400A by the NEC the utility might not rate this as a 400A service. Get the service rating from the utility and use that to base the back feed on.
Posting Permissions
  • You may not post replies
  • You may not edit your posts