    Trunk Line Circuits

    Anyone familiar with Class X trunk line circuits. I think it's a network riser. They never indicated the # or size of wires.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Riser.jpg 
Views:	110 
Size:	8.0 KB 
ID:	20189   Click image for larger version. 

Name:	Trunk SLC Class X.jpg 
Views:	58 
Size:	19.9 KB 
ID:	20190  

  2. #2
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,704
    Quote Originally Posted by mstrlucky74 View Post
    Anyone familiar with Class X trunk line circuits. I think it's a network riser. They never indicated the # or size of wires.
    So, what bonehead put that 15 foot requirement AND 2-hour resistance on the same sheet? Is this a NYC project?

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,994
    Quote Originally Posted by gadfly56 View Post
    So, what bonehead put that 15 foot requirement AND 2-hour resistance on the same sheet? Is this a NYC project?

    Yes

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,704
    Quote Originally Posted by mstrlucky74 View Post
    Yes
    Are you merely bidding it or did your company design it?

    The 15 foot separation is intended to allow the use of Class A or X circuits without 2-hour fire rated cable where Survivability Level 2 is required. Here are some pertinent snips:

    760.53 Fire Alarm Circuit Integrity (CI) Cable. Cables suitable for use in fire alarm systems to
    ensure survivability of critical circuits during a specified time under fire conditions shall be listed
    as circuit integrity cable. Cables so identified shall have the classification “CI-NYC certified fire
    alarm cable”


    The immediate problem is nobody makes this. You might as well spec unicorn farts. Which is why the following is in Appendix Q, modifying NFPA 72:

    24.3.5.4.1 Add the following exception: Exception -Pathway survivability Level 1 is permitted when pathway is designated as Class A or Class X with redundant pathways separated by a minimum of 15 feet.

    And this is what it modifies:

    24.3.5.3* The pathway survivability requirements in 24.3.5.4
    through 24.3.5.12 shall apply to notification and communications
    circuits and other circuits necessary to ensure the continued
    operation of the emergency communications system.
    24.3.5.4 In-building fire emergency voice/alarm communications
    systems shall comply with 24.3.5.4.1 or 24.3.5.4.2.
    24.3.5.4.1 For systems employing relocation or partial evacuation,
    a Level 2 or Level 3 pathway survivability shall be
    required.
    24.3.5.4.2 For systems that do not employ relocation or partial
    evacuation, a Level 0, Level 1, Level 2, or Level 3 pathway
    survivability shall be required.

  5. #5
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,994
    Quote Originally Posted by gadfly56 View Post
    Are you merely bidding it or did your company design it?

    The 15 foot separation is intended to allow the use of Class A or X circuits without 2-hour fire rated cable where Survivability Level 2 is required. Here are some pertinent snips:

    760.53 Fire Alarm Circuit Integrity (CI) Cable. Cables suitable for use in fire alarm systems to
    ensure survivability of critical circuits during a specified time under fire conditions shall be listed
    as circuit integrity cable. Cables so identified shall have the classification “CI-NYC certified fire
    alarm cable”


    The immediate problem is nobody makes this. You might as well spec unicorn farts. Which is why the following is in Appendix Q, modifying NFPA 72:

    24.3.5.4.1 Add the following exception: Exception -Pathway survivability Level 1 is permitted when pathway is designated as Class A or Class X with redundant pathways separated by a minimum of 15 feet.

    And this is what it modifies:

    24.3.5.3* The pathway survivability requirements in 24.3.5.4
    through 24.3.5.12 shall apply to notification and communications
    circuits and other circuits necessary to ensure the continued
    operation of the emergency communications system.
    24.3.5.4 In-building fire emergency voice/alarm communications
    systems shall comply with 24.3.5.4.1 or 24.3.5.4.2.
    24.3.5.4.1 For systems employing relocation or partial evacuation,
    a Level 2 or Level 3 pathway survivability shall be
    required.
    24.3.5.4.2 For systems that do not employ relocation or partial
    evacuation, a Level 0, Level 1, Level 2, or Level 3 pathway
    survivability shall be required.
    Much appreciated. Well they are showing the trunk line/network riser rising up in a shaft. How they hell could you have 15' separation between the sending and return?

    I'm told by my FA vendor the network riser always has to be run on 2 hour rated cable.

  6. #6
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,704
    Quote Originally Posted by mstrlucky74 View Post
    Much appreciated. Well they are showing the trunk line/network riser rising up in a shaft. How they hell could you have 15' separation between the sending and return?

    I'm told by my FA vendor the network riser always has to be run on 2 hour rated cable.
    Ask them where they get their NYC approved CI or CIC. Request the manufacturer's catalog number. They will never get you a good answer.

  7. #7
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,994
    Quote Originally Posted by gadfly56 View Post
    Ask them where they get their NYC approved CI or CIC. Request the manufacturer's catalog number. They will never get you a good answer.
    See attached.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Capture.jpg 
Views:	30 
Size:	17.0 KB 
ID:	20211   Click image for larger version. 

Name:	Capture2.jpg 
Views:	24 
Size:	16.9 KB 
ID:	20212  

  8. #8
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,704
    Quote Originally Posted by mstrlucky74 View Post
    See attached.
    VITALink® does not meet the requirements of Local Law 39.

    From Local Law 39:

    760.53 Fire Alarm Circuit Integrity (CI) Cable. Cables suitable for use in fire alarm systems to
    ensure survivability of critical circuits during a specified time under fire conditions shall be listed
    as circuit integrity cable. Cables so identified shall have the classification “CI-NYC certified fire
    alarm cable”

    From the approval:

    54502 17A0167 Requesting approval for use in New York City of your Wire/Cable FHIT .40A Model/Series : VITALink(R) 2 Hour Fire Resistive CIC
    Line; FHIT .40A Approved $200.00
    Disclaimer: Advisory Board approval is limited to materials received and reviewed by the Board. Contact Con-Edison regarding Blue Book requirements.

    The CIC is for EMT. You'll note from the FAQ that the product may NOT be installed in IMC or RMC. Fire alarm cable in most areas in NYC has to be in RMC.

    The VITALink® product is OK for other than fire alarm 2-hr fire resistive uses.

  9. #9
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,994
    Gad really appreciate your feedback. I'm a little lost. The network riser/trunk line has to be 2 hour rated. And the conduit is run exposed so it has to be RGS. So how would you accomplish that if the vitalink wont suffice? Although I guess if the closet is two hour rated and dedicated to fire alarm we should be ok without 2 hour rated cable. Thanks.

  10. #10
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    5,704
    Quote Originally Posted by mstrlucky74 View Post
    Gad really appreciate your feedback. I'm a little lost. The network riser/trunk line has to be 2 hour rated. And the conduit is run exposed so it has to be RGS. So how would you accomplish that if the vitalink wont suffice? Although I guess if the closet is two hour rated and dedicated to fire alarm we should be ok without 2 hour rated cable. Thanks.
    ^^^^That right there would cover you.