User Tag List
Results 1 to 8 of 8
Thread: MCC's with fuses or molded case breakers
  1. #1
    Join Date
    Apr 2008
    Posts
    375
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We are having a debate at our site on the safety aspects of using MCC's with fused disconnect vs disconnect that use a molded case breaker. My belief is the fused disconnects are safer as I have a visual indication that the stabs have disengaged...can't tell on the molded case breaker. I know I should test the circuit with a meter on both types of disconnects. It will interesting to see other opinions on this subject. As always many thanks in advance.
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,183
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by cornbread View Post
    The visual verification maybe gives a little more safety feature to that setup. Unless there is an inspection window on the door you still must treat it as though it were live when opening the door to inspect.
    I live for today, I'm just a day behind.
  3. #3
    Join Date
    Mar 2003
    New York
    Posts
    1,793
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Live/dead/live with ppe on.
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,383
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It does not really matter. You still have to test to prove it is open even if you can see it.
    I personally have gone away from fuses above 100A or so. Too many times there are no spares and they are not all that easy to come by at 3 am on a sunday morning.
    Bob
  5. #5
    Join Date
    Jul 2015
    Soldotna, AK, USA
    Posts
    133
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yeah the knives can be disengaged and also be fed from the bottom, making knives hot...
    Always check top and bottom on everything seen broken breaker handles on molded case breakers that looked like they were off but the plastic handle broke internally...
  6. #6
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,715
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    I agree, so the point is moot.
    Fuses can also lead to single phasing, unless you want to put phase fail monitors in every bucket. Now it just got more complicated.
    I like breakers.
  7. #7
    Join Date
    Jul 2006
    Posts
    8,496
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Cow View Post
    I like breakers.
    These cover where I fall; visual indication is irrelevant anyway, Test-Verify-Test still rules the safety roost and despite the rhetoric from fuse mfrs on how much better fuses are, the risks / hassle factor outweighs the benefits to me. I’ve never once seen a piece of EMT used in lieu of a circuit breaker, but I can’t even count how many times I have seen it used as a fuse. The temptation is too great when the production mgr is screaming at you about how he is going to miss his bonus because you don’t have the right fuse at hand...
    That said, if you have more than 100kA available fault current, you will have issues finding small breakers for buckets suitable for that use. But in 40 years, I have never once come across an MCC needing even more than 65kA. I’ve heard people discuss it as if it’s a thing, never come across it.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  8. #8
    Join Date
    Apr 2008
    Posts
    375
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Surprised by the responses. I realize checking the circuit is required, but I like the visual indication that the stabs are dis-engaged. I have no way of knowing what going on inside the molded case breaker...it was off when I checked it, but internally ... could it fail while I'm working in the bucket (un-likely) but I have no visual indication of anything going wrong. That's why I like the visual indication of open stabs.