strange instructions

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
My guess is that the instructions tell the installer how to enable the non-interchangeability lockout, and if left for the owner to examine would allow them to defeat that provision and install cheaper breakers.
Just a SWAG.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It would probably be easier to guess the reason for that warning if we could see the rest of the instructions. The part that we see on the first sheet does not seem particularly interesting. :)
 

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
It would probably be easier to guess the reason for that warning if we could see the rest of the instructions. The part that we see on the first sheet does not seem particularly interesting. :)
sheet was tore but I think you are right about non-interchangeability.


so if I had put the panel in, and used screws to mount instead of nails, I would be in violation due to manufacturers instructions?:)
 

ADub

Senior Member
Location
Midwest
Occupation
Estimator/Project Manager
so if I had put the panel in, and used screws to mount instead of nails, I would be in violation due to manufacturers instructions?:)

Im positive some people on this site would say yes


Sent from my iPhone using Tapatalk
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
sheet was tore but I think you are right about non-interchangeability.


so if I had put the panel in, and used screws to mount instead of nails, I would be in violation due to manufacturers instructions?:)
That is always a good topic for controversy here on the Forum.
It would seem to depend on whether the particular instructions in question are part of the listing approval of the product.
Some instructions are critical to safety and may have been evaluated by the NRTL as part of the listing process. Others are not safety critical and some of the material that comes with the product is more marketing than instructions.

You be the judge, and then the AHJ will be the higher court.

I wonder if an inspector could ask for proof that you destroyed the instructions and could red tag you if they were left in the panel?
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Take notice of the reference to the NEMA recommended method for removing the knockouts. The illustrations and instructions came from NEMA Engineering Bulletin No. 55 that was first published in 1954.

This Bulletin is still available to this very day here: http://www.nema.org/Technical/Documents/Bull_55_reaffirmed_12_15_111.pdf

Great link but, having read them.....

#1 assumes the center knockout is only attached on one side.

How do you get from #2 to #3 without busting out the other rings? Especially if you have to place the linesman pliers on top of another knockout, risking punching that through?

I have tried the 'NEMA' way more than once. Sometimes it works, other times it doesn't. Maybe paint was thinner and dies were sharper in 1954.
 

iwire

Moderator
Staff member
Location
Massachusetts
I have tried the 'NEMA' way more than once. Sometimes it works, other times it doesn't. Maybe paint was thinner and dies were sharper in 1954.

Exactly.

To be fair it must be tough to keep the dies set correctly. I imagine there is not much range between falling out and never coming out.
 