T8 LED Retrofit

Status
Not open for further replies.
Client tried two different brands of 32W rapid & instant-start LED tubes (first from big on-line distributor, then some Philips tubes from HD) in their bigbox two-tube fixtures.

Neither worked despite fixtures being clearly labeled for any rapid start T8.

The Sylvania 32W T8's he'd started with a year ago work fine.

Any thoughts on what's going on? So far haven't heard back from fixture manufacturer
 

Galt

Senior Member
Location
Wis.
Occupation
master electrician and refrigeration service tech.
T8 needs a ballast the retrofits are line voltage. If I understand what you are saying.
 

Barbqranch

Senior Member
Location
Arcata, CA
Occupation
Plant maintenance electrician Semi-retired
We had a problem w/ Philips T8 size LED replacements when we changed from 32 W fluorescents in some of the fixtures. When they were retrofitted from magnetic ballasts years earlier, some of them only had one wire to the tombstone. The 32 W fluorescent tubes don't care, but the Philips tube only used one pin on each end, and if that one wasn't connected, . . .
 