    Please see attached picture.
    label Information: "Through Bus" = 800A Section Amps = 600 Max.
    Want to confirm for 120% rule that "Through Bus" = Nameplate Rating.
    Thanks
    MJR
  2. #2
    Join Date
    May 2011
    Posts
    4,860
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I wouldn't confirm that. Ask the AHJ.
    Looks like you've got a 'multiple ampacity' busbar which if in California under the 2014 NEC (equivalent) can be interconnected to under 'engineering supervision.'
  3. #3
    Join Date
    Nov 2015
    CA, USA
    Posts
    715
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Through bus is the horizontal bus that connects the sections together. Section bus runs vertically in a section and is what supplies whatever is connected to the bus in that section. If you land a back feed breaker in the section then the bus rating is 600A for the 120% rule. For more info see this: http://electrical-engineering-portal...siemens-basics
    Probably not what you were hoping for.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by pv_n00b View Post
    I don't do PV stuff, but agree - depends if you are feeding into the 800 amp main bus or into a 600 amp section bus.
    I live for today, I'm just a day behind.
  5. #5
    Join Date
    May 2011
    Posts
    4,860
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    To invoke the 120% rule you have to be at the opposite end of the busbar, which arguably isn't possible when you have multiple busbar sections coming off the main bus, presumably without individual OCPD. (i.e. you can't be at the opposite end of all those busbars) I think best case is that the main switch gear OCPD is not more than 600A and the AHJ lets you tie into the opposite end of the 600A section that is at the opposite end. I assume there is a stipulation that each 600A bus section can't have more than 600A load, and if that's followed then the logic behind the rule would deem such an installation safe. But article 705 doesn't explicitly address that. Probably it just needs an engineer to sign off on the details that simple code rules (or not-so-simple code rules, as the case may be) just can't fully address.
  6. #6
    Join Date
    Nov 2015
    CA, USA
    Posts
    715
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I agree, once you start interconnecting to switchboards there are few simple rules of thumb anymore. Switchboards are too highly customizable and you need to understand how that specific switchboard is put together. I've seen weird stuff out there. I've talked to many contractors who just default to supply-side interconnections because they don't want to get involved in what is going on in there, I don't agree with that choice but many do it.
  7. #7
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,408
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Why not? Supply side interconnections are frequently much simpler to design and install. They are just as legal and safe as load side connections. If the input OCPD in the switchgear happens to have space on its input bus to land PV connectors, it's easy-peasy.
  8. #8
    Join Date
    Nov 2015
    CA, USA
    Posts
    715
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ggunn View Post
    How many have you done where you used a landing point that was labeled "tap" and not just some convenient hole or stud that happened to be there? How many people drill holes in bus to land PV conductors? It might seem easy to do, but it's not easy to do correctly.
    https://www.ul.com/global/documents/...ns/april10.pdf
  9. #9
    Join Date
    Jul 2017
    Chico, CA, USA
    Posts
    21
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Answer
    Thanks,
    Just to be on the safe side of the rule. I'll treat this as 600A.
    I'll have to de-rate the main to get me under the rule.
    I'll also look to the manufacturer to see if they have Tap Locations on the Main Bussing.
    Michael
  10. #10
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,408
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have never drilled a hole in a bus to land PV connection terminals. I have found open holes just like the ones the service conductor terminals are landed on and gotten the OK from the switchgear manufacturer to use them for PV interconnection.
Tags for this Thread