User Tag List
Results 1 to 4 of 4
Thread: Can you ID this (what I assume is a) Heat Detector?
  1. #1
    Join Date
    Mar 2010
    Posts
    285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It looks like it is connected to a Honeywell Vista system and active.
    Otherwise I would have said it is old and ignored it.
    Can you identify it?
  2. #2
    Join Date
    Mar 2003
    New York
    Posts
    1,908
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Got a ladder or zoom lens?
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    25,440
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    It is a temperature sensor, with the metal "hat" to make it more sensitive via additional surface area. The only info missing is the temperature at which it switches, but that should be marked on the unit.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    May 2018
    California
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It looks like a temperature detector or you can say heat detector as well.
    But it kinda looks old. I don't think these type of sensors are now available in the market.