    2 HR FA AREAS

    Why the heck would they call for ALL wiring to be 2 hour rated even in sprinkler protected areas?
    Attached Images Attached Images  

  2. #2
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,763
    Quote Originally Posted by mstrlucky74 View Post
    Why the heck would they call for ALL wiring to be 2 hour rated even in sprinkler protected areas?
    Purely opinion , but I think the intent of this note is to require 15 feet of separation between conductors and calling that separation (2 hours) probably comes from some guide book. Normally 5 feet is an acceptable separation or horizontal runs.


    I know what I don't know, and I know where to go to find it!

  3. #3
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,453
    would locating standard cable behind a 2 plus hour rated wall be acceptable? Aside from Mi cable, I am not aware of any wire or method that would still function in a fire
    Electricians do it until it Hertz!

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,127
    Quote Originally Posted by JFletcher View Post
    would locating standard cable behind a 2 plus hour rated wall be acceptable? Aside from Mi cable, I am not aware of any wire or method that would still function in a fire
    VITALink® CIC would do it, but it doesn't meet some of the other requirements for NYC.

  5. #5
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,235
    What dies the 15' separation have to do with a 2 hour rating?

  6. #6
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,127
    Quote Originally Posted by mstrlucky74 View Post
    What dies the 15' separation have to do with a 2 hour rating?
    For certain occupancies, where the fire response is NOT immediate and total evacuation (airport, high rise), the notification devices must remain operable for 2 hours, along with anything else that facilitates their operation (Pathway Survivability Level 2). Normally you'd use VITALink or a similar product. In NYC, none of those products meet some of the other requirements of Local Law 39, so the city has crafted this alternative: Install the circuits as Class A AND separate not by 4 feet but by 15 feet, and we'll consider it the equal of Pathway Survivability Level 2. The exception is NOT supposed to use 15 foot separation and a 2-hour rated cable.

  7. #7
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,235
    Quote Originally Posted by gadfly56 View Post
    For certain occupancies, where the fire response is NOT immediate and total evacuation (airport, high rise), the notification devices must remain operable for 2 hours, along with anything else that facilitates their operation (Pathway Survivability Level 2). Normally you'd use VITALink or a similar product. In NYC, none of those products meet some of the other requirements of Local Law 39, so the city has crafted this alternative: Install the circuits as Class A AND separate not by 4 feet but by 15 feet, and we'll consider it the equal of Pathway Survivability Level 2. The exception is NOT supposed to use 15 foot separation and a 2-hour rated cable.

    So it's one or the other?

  8. #8
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,763
    Quote Originally Posted by mstrlucky74 View Post
    So it's one or the other?

    No, it is the one, 15 feet of separation.


    I know what I don't know, and I know where to go to find it!

  9. #9
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,127
    Quote Originally Posted by Strathead View Post
    No, it is the one, 15 feet of separation.
    Plus Class A.

    If you could find cable complying with LL 39 and being 2-hr fire resistive you could use it without Class A as NYC does not require everything to be Class A. The Port Authority, NJ Transit, LIRR, MTA, etc usually have internal standards that do require Class A, but the NYC code does not.