User Tag List
Page 3 of 9 FirstFirst 1 2 3 4 5 ... LastLast
Results 21 to 30 of 81
Thread: Voltage Unbalance Reason
  1. #21
    Join Date
    Feb 2013
    India
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ingenieur View Post
    +(vab = 25 + 175j) or 175/82-(vac = 25 - 175j) or 175/-82-(vbc = 0 + 350j) or 350/90= 0 + 0jsomething does not computeone machine in reverse rotationmessed up connectionsetc or some combination
    The generator voltage sequence is Vab, Vbc, Vca and their vector sum equals zero. But in your calculation Vac instead of Vca used. So perhaps reverse connection in one phase may also be a reason...
  2. #22
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    using abc
    a 600/0
    b 600/-15
    c 600/15
    ab = 20+155j = 156/82
    bc = 0-310j = 310/-90
    ca = -20+155j = 156/98
    sum = 0
    no real change
    no idea what is going on
  3. #23
    Join Date
    Feb 2013
    India
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    using abc
    a 600/0
    b 600/-15
    c 600/15
    sum = 0
    no real change
    One solution to the part of the riddle is the generator is ungrounded and so phase to neutral voltage may be anything, around 590V in the OP case. Another is if the actual voltage readings of the OP are taken, I think their vector sum may not be zero and so there may be a break in windings or one phase winding may be reverse connected and that is my stand.
  4. #24
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,465
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    I don't understand, if the neutral is kept floating, then aren't any line to neutral voltage readings meaningless?
    No. Phase and neutral voltage to ground readings are meaningless.
  5. #25
    Join Date
    Aug 2008
    San Francisco
    Posts
    753
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    using abc
    a 600/0
    b 600/-15
    c 600/15
    sum = 0
    no real change
    The reason you can't make any sense of it is because the readings are meaningless on an ungrounded wye as others have stated over and over!
    Am I in shape?? I get plenty of exercise pushing my luck!!
  6. #26
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ATSman View Post
    you will get a reading thru capacative couple, because he DID get reading
    regardless, ph-n will not be 3x ph-ph
  7. #27
    Join Date
    Jul 2006
    SE USA as far as you can go
    Posts
    2,733
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The OP has left the discussion; so in other words it's all speculation after post #5.
    "Just because you're paranoid, doesn't mean they're not out to get you"
  8. #28
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    we know a few things
    only occuring on 1 bus
    VLL = 150-300 (2 @ 150, 1 @ 300), VLN = 600, VLN ~ 2-4 x VLL
    we know what the ph ang must be to result in these magnitudes
    it is not cool for an op to make a post asking a question about an issue (especially an implausible one like this) and not providing feedback
  9. #29
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    That's been my main gripe with people posting questions on this form since its inception. People post the weirdest things, everyone brainstorms possible problems and solutions, and the o p rarely gets back to post what the problem was and how or if it was solved. C'est la vie...
  10. #30
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,465
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    But we have a lot of fun speculating and arguing, don't we?
Posting Permissions
  • You may not post replies
  • You may not edit your posts