    Supporting fire alarm cable to existing fire alarm conduit

    Is it acceptable to support Plenum rated fire alarm cable to an existing dedicated for alarm conduit?

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,541
    No. 760.46 references 300.11 and 300.11(C) says raceways cannot be used to support cables.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  3. #3
    Join Date
    Nov 2015
    Location
    Merchantville, Camden County New Jersey
    Posts
    9
    Unless they are part of the same system


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,082
    Quote Originally Posted by Current Eddy View Post
    Unless they are part of the same system
    Code Reference?

    Roger
    Moderator

  5. #5
    Join Date
    Nov 2015
    Location
    Merchantville, Camden County New Jersey
    Posts
    9
    Quote Originally Posted by roger View Post
    Code Reference?

    Roger
    760.143 Support of Conductors.
    Power-limited fire alarm circuit conductors shall not be strapped, taped, or attached by any means to the exterior of any conduit or other raceway as a means of support.

    Sorry couldn’t find it