    I am doing a small renovation job in which there is existing two conductor BX cable in the house with no ground except the BX cable. The building inspector wants the box grounded with the wire to the new outlets. Are those green grounding clips that clip on the edge of the box OK? Or does the boxes have to be drilled and tapped and a ground wire screwed in?
    I appreciate your help.
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Fredkehoe View Post
    the clips are UL listed for that purpose.
    Bob
  3. #3
    Join Date
    Aug 2017
    Cornwall ny USA
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    OK, thank you very much for your speedy reply.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,595
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Either method will work but I would just use a self-grounding receptacle and forget the bonding jumper.
    Rob
  5. #5
    Join Date
    Aug 2017
    Cornwall ny USA
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Thats a good idea too.
  6. #6
    Join Date
    Mar 2003
    Vermont
    Posts
    1,946
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's somewhat debatable as to BX is an ECG , as it was not manufactured to be one in the first place
    I'd just go with 406.4D, park a DF in the panel ,and use any old crappy receptacle outlet....
    ~RJ~
  7. #7
    Join Date
    Mar 2016
    The Motor City, Michigan USA
    Posts
    969
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ... do the boxes have to be drilled and tapped ...
    A combination drill-tap makes it fast & easy:
  8. #8
    Join Date
    Oct 2015
    US
    Posts
    789
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    In NYC even if you use self grounding receptacles you need install a ground tail to the box via a threaded screw, most supply houses around here stock 1900 boxes (4x4) steel boxes with the ground screw already installed some even with the wire to
    Sent from my SM-G950U using Tapatalk
  9. #9
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,595
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nickelec View Post
    I believe that you're incorrect can you show me that code requirment?
    Rob
  10. #10
    Join Date
    Oct 2012
    nyc
    Posts
    312
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    That's what can give you extra 'points' to pass inspection. Not a code requirement.
    Devil in the detail is that if the box or mud ring is recessed more than 1/4" self grounding clip is not (as much) effective but grounding pigtail is. Grounding path is even worse when you replace the 6/32 screw with a longer one and install switch box extender (goof ring, add a depth adapter, collar).
    Self grounding receptacles on powder coated surface 'mulberry' covers require grounding pigtail.
    So it is just easier to install a grounding pigtail every time and tell everybody to do so around here.