Page 1 of 2 12 LastLast
Results 1 to 10 of 20

Thread: Glowing LED Lamp

  1. #1
    Join Date
    Dec 2005
    Location
    WI & AZ
    Posts
    2,085

    Glowing LED Lamp

    Going on a service call tomorrow where the customer states that an LED lamp slightly glows when the switch is in the off position. Any thoughts?
    Tom

    " And all the science I don't understand, it's just my job five days a week "

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,766
    Last time I did a call like that it was a dimmer switch that did not have a full off and it let enough power through to make the LED glow just slightly.
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,194
    Yeh same ..... those Lutron dimmers that have an air-gap switch at the bottom can do that.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    Not first time this question has come up here - illuminated wall switch could also allow enough current to pass through when open to allow some illumination of the LED.
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Dec 2005
    Location
    WI & AZ
    Posts
    2,085
    After checking this out, looks like a faulty lamp. It was a 4 lamp ceiling fan light fixture and one of the lamps had a slight glow no matter which socket it was installed in. Told the HO to get new lamps. Weird............
    Tom

    " And all the science I don't understand, it's just my job five days a week "

  6. #6
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    3,260
    All of the 4' 'shoplight' type fixtures that I get from costco have a very slight glow when they are turned off by their built in pull switch. Unplugging them turns them off completely. I figure there is some leakage through something like an MOV across the switch, or capacitive coupling or something similar.

    I remember a design project that I had with some high intensity LEDs. At the time I was surprised by how much light they produced when driven at well below the datasheet 'turn on' threshold voltage. Very little current will make an LED noticeable in a dark room.

    -Jon

  7. #7
    Join Date
    Jul 2018
    Location
    Freeport IL
    Posts
    1

    lutron dimmers

    or if this is on occupancy sensor.

  8. #8
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    7,037
    180723-2032 EDT

    A/A Fuel GTX:

    You do not have a defective bulb. You have not found the cause of the problem.

    If there is no current to the bulb, then there will be no light. Somehow sufficient current gets to the bulb when you think it is turned off.

    .

  9. #9
    Join Date
    Aug 2012
    Location
    Changed for anonymity
    Posts
    281
    My first experience with one of these not long ago and it was a loose neutral....My wrists love em' but you can keep your wego's

  10. #10
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,838
    Quote Originally Posted by RLyons View Post
    My first experience with one of these not long ago and it was a loose neutral....My wrists love em' but you can keep your wego's
    Are you sure you're replying to the right thread/post?