    Exits Feed from Normal Panel

    Have exits feed from normal panel in hospital. There is no ATS feeding panel. Find it a little odd an maybe even against code that they are fed from normal panel. Think it's considered life safety.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,156
    Are they battery backup?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by infinity View Post
    Are they battery backup?
    +1
    I live for today, I'm just a day behind.

  4. #4
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,276
    Yes, arent all?

  5. #5
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,367
    Quote Originally Posted by mstrlucky74 View Post
    Yes, arent all?
    No they aren't. If they are battery back up fixtures they have to be fed from the normal branch, they have to be fed from the local lighting circuit.

    Roger
    Moderator

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by roger View Post
    No they aren't. If they are battery back up fixtures they have to be fed from the normal branch, they have to be fed from the local lighting circuit.

    Roger
    Which may or may not be on an emergency panel, local circuit must fail before battery takes over.
    I live for today, I'm just a day behind.

  7. #7
    Join Date
    Dec 2010
    Posts
    1,427
    Quote Originally Posted by roger View Post
    they have to be fed from the local lighting circuit.
    I don't think that is true.
    The more they overthink the plumbing, the easier it is to stop up the drain

  8. #8
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,367
    Quote Originally Posted by dkidd View Post
    I don't think that is true.
    You need to read 700.12(F) then.

    Roger
    Moderator

  9. #9
    Join Date
    Dec 2010
    Posts
    1,427
    Exit signs are not unit equipment.
    The more they overthink the plumbing, the easier it is to stop up the drain

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by dkidd View Post
    Exit signs are not unit equipment.
    Some are some aren't.

    If required to be illuminated during normal power failure, then likely considered part of emergency lighting system, though there are signs that don't even require power these days to be visible in low to no light conditions
    I live for today, I'm just a day behind.