    Energizing on Set Time Schedule

    Several years ago, a worker on my construction project, was completing work on a transformer when he was electrocuted. Very tragic-dramatic event. The investigation revealed that the upstream energization of the transformer was based of a set time. Worker was triying to complete the work befroe the time deadline and/or he did not have the correct time. Investigation also revealed that the group responsible for commissioning were not provided with portable radios or telephones. A phone or radio could have been used to effectively communicate with other team members the status of completed work before energization.

    Is electrical energization based on set time schedule(s) prohibited by any law or consensus standard? If so where is the subject is clearly addressed? Any comments will be appreiciated.

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,139
    It sounds like the practice common to utility work of setting local grounding jumpers on deenergized source wires would have prevented this tragedy. Not, AFAIK, mandated by NEC or OSHA though.

    Sent from my XT1585 using Tapatalk

  3. #3
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,534
    IMHO, this was a failure to properly lockout/tagout before working on the equipment.
    Bob

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,288
    Quote Originally Posted by petersonra View Post
    IMHO, this was a failure to properly lockout/tagout before working on the equipment.
    Maybe. If it were new construction at what point does one have to start to consider the possibility of what you are working on becoming energized and need to LOTO?

    As mentioned for utility work or other similar situations - local grounding jumpers is very important, without them one about has to treat it as if it were energized.
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,277
    Quote Originally Posted by petersonra View Post
    IMHO, this was a failure to properly lockout/tagout before working on the equipment.
    I agree. Though I have no idea how the Poco does their work, anytime my hands are in something that could be energized, my locks are on any and all applicable breakers. Getting hit with 120 is no fun, getting hit with 19920 V, probably the last thing you ever do
    Electricians do it until it Hertz!

  6. #6
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,418
    Energizing on set time schedule without any safeguard is like working under a time bomb set to go off at a time schedule. No law/code/standard will allow such a work practice.

  7. #7
    Please identify the specific law you are referring too. Info needed for a safety bulletin I am preparing on the subject.

  8. #8
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,418
    Quote Originally Posted by TVH View Post
    Please identify the specific law you are referring too. Info needed for a safety bulletin I am preparing on the subject.
    Refer to CFR 29 subpart S 'Electrical' of OSHA. The OSHA requires the equipment used, in your case the equipment for energizing on set time schedule for power line work, to be certified so by a third party.

  9. #9
    Join Date
    May 2018
    Location
    bamenda,cameroon
    Posts
    2
    i found myself in a similar problem 02 years ago. the procedure of lockout was not respected and consequently the workplace was not safe enough to work in. these type of problems are very common in construction sites