    Several years ago, a worker on my construction project, was completing work on a transformer when he was electrocuted. Very tragic-dramatic event. The investigation revealed that the upstream energization of the transformer was based of a set time. Worker was triying to complete the work befroe the time deadline and/or he did not have the correct time. Investigation also revealed that the group responsible for commissioning were not provided with portable radios or telephones. A phone or radio could have been used to effectively communicate with other team members the status of completed work before energization.
    Is electrical energization based on set time schedule(s) prohibited by any law or consensus standard? If so where is the subject is clearly addressed? Any comments will be appreiciated.
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,129
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    It sounds like the practice common to utility work of setting local grounding jumpers on deenergized source wires would have prevented this tragedy. Not, AFAIK, mandated by NEC or OSHA though.
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,366
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IMHO, this was a failure to properly lockout/tagout before working on the equipment.
    Bob
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,124
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    Maybe. If it were new construction at what point does one have to start to consider the possibility of what you are working on becoming energized and need to LOTO?
    As mentioned for utility work or other similar situations - local grounding jumpers is very important, without them one about has to treat it as if it were energized.
    I live for today, I'm just a day behind.
  5. #5
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree. Though I have no idea how the Poco does their work, anytime my hands are in something that could be energized, my locks are on any and all applicable breakers. Getting hit with 120 is no fun, getting hit with 19920 V, probably the last thing you ever do
  6. #6
    Join Date
    Feb 2013
    India
    Posts
    2,654
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Energizing on set time schedule without any safeguard is like working under a time bomb set to go off at a time schedule. No law/code/standard will allow such a work practice.
  7. #7
    Join Date
    Nov 2005
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Please identify the specific law you are referring too. Info needed for a safety bulletin I am preparing on the subject.
  8. #8
    Join Date
    Feb 2013
    India
    Posts
    2,654
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TVH View Post
    Refer to CFR 29 subpart S 'Electrical' of OSHA. The OSHA requires the equipment used, in your case the equipment for energizing on set time schedule for power line work, to be certified so by a third party.
  9. #9
    Join Date
    May 2018
    bamenda,cameroon
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    i found myself in a similar problem 02 years ago. the procedure of lockout was not respected and consequently the workplace was not safe enough to work in. these type of problems are very common in construction sites
  10. #10
    Join Date
    Nov 2005
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ADDITIONAL INPUTS TO COMMENTS ON "ENERGIZATION ON SET TIME SCHEDULE"
    I failed to mention in the original post that locks and tags were removed from the prime energy source by supervision prior to the initial energization of the new field transformer. The lone worker at the transformer did not have a lock applied to the energy source. Part of the energization procedure, at that time, allowed energization based on a set time schedule. The procedure which was approved by management, had been in place for several projects without incident. The lone worker had not completed all his work and it was speculated that he did not have the proper time. It is obvious that the procedure was seriously flawed and it was subsequently revised requiring radio or portable telephone communications at the equipment being energized before the switch was pulled at the substation. Other safeguards were also added to the procedure.
    Although the answers to my previous posts were good and interesting, the issue I wanted to address is the identification of any recognized standard that prohibits the energization of field equipment based on a set time schedule. I cannot locate a reference on this subject. Can anyone help identify a mandatory standard/reference on this subject. I believe the subject needs highlighting to operatives responsible for the electrical energization of field positioned equipment.
    Thank you for your assistance and cooperation.