    We have 4 main 480 services coming into our plant . These range from 4000 amp to 1600 amp . We have bolt-loc switches and molded case SQ D circuit breakers on them . They all have Incident energy level of ( 173 cal/cm at working distance of 1 ft 6 in ) . The PPE level - site-specific says " PROHIBITED " . ( Arc Flash Boundary is 31 ft 2 in ) . I use the PPE we have which is rated 25 Cal's when opening or closing a breaker or switch . Is PPE required to operate a breaker or switch ? If it says "PROHIBITED " is this saying that we must use a remote switch actuator ?
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,250
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Davebones View Post
    The term Prohibited is not in NFPA70E. Many, if not most, companies have chosen to prohibit 'work' on equipment >40 cal/cm^2, per their Electrical Safe Work Practices program.
    Before I go any further.
    How often have your bolted pressure switches been operated, daily, yearly, never?
    How often are your switches been maintained, cleaned and lubricated? I think manufacturers recommend every 5 yrs.
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    May 2007
    Westminster, MD
    Posts
    653
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Normal Condition
    Davebones,
    As long as the equipment is in normal condition it can be operated without PPE based on table 130.5(C).
    The Normal definition includes properly maintained, which is where much equipment falls short of being Normal. Most electrical testing companies that I've dealt with put a dated sticker on the gear after performing maintenance.
  4. #4
    Join Date
    Jul 2006
    Posts
    8,496
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The incident energy levels and approach boundaries apply to EXPOSED conductive elements. Operating with the doors closed, although still risky for equipment that is NOT rated as Arc Resistant (but properly maintained as mentioned above), should not be assigned the same risk level. What you are seeing is likely a “lazy man’s” risk assessment technique. CYA by forbidding any interaction.
    In my opinion this attitude is actually leading to MORE risk because people tend to ignore equipment they are afraid to use. As someone put it to me yesterday when discussing this, “Our switchgear is basically a fuse now. We can’t go near it, we can’t shut it down or test it, so the only time we can inspect, maintain or repair it is after something blows up.”
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  5. #5
    Join Date
    Jul 2008
    North Of Tampa Fl
    Posts
    461
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We've had the switchgear cleaned and tested roughly every 5 years on . It's in a air conditioned environment . I understood that as long as you have maintained it you ( 70E ) said you can operate it . I choose to use the PPE as a extra precaution . I asked the question as with some of the previous posts I've seen it can get confusing about PPE and operating a switch or a breaker . The sticker " PROHIBITED " was put on it after we had the arc flash study done .
  6. #6
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,816
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Then you technically don't need PPE per 70E with the doors closed for normal operations. But resetting it after a fault for example would not be normal so PPE should be worn (Or remote operators)
  7. #7
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    370
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    With such a high IE, I am curious to know if the utility actual available fault current was used or was it an infinite bus fault current at the transformer secondaries?
    If modeled with utility actual available fault currents and utilizing the utility protective device on the primary side, your values may be lower.