    Quote Originally Posted by gar View Post
    180511-1429 EDT
    An important concept is that the sum of two sine waves of identical frequency and that are phase related create a sine wave of the same identical frequency and with some possibly different phase relative to one of the original waves.
    .
    Yes I think that is the key, and how you choose to represent it graphically. Metering line to line could be thought of as just a "regular" single sine function. In this case, the x-axis is one line while the sine wave is the other line. But it could also be graphed as two sine functions, one reflected over the x- axis to make the second one. As gar said, that is mathematically the same as the first case and could be redrawn as such. In this case the x-axis is the center tap. Expressing it with the two functions illustrates the center tap to lines readings better.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #12
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,235
    Just to make sure my explanation was clear, I graphed the two methods in Maple. Yes, I took the 120 and 240 to be peak not RMS, and I didnt scale the x-axis to standard frequency.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	single.jpg 
Views:	55 
Size:	126.8 KB 
ID:	20312   Click image for larger version. 

Name:	two.jpg 
Views:	52 
Size:	138.0 KB 
ID:	20313  
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #13
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,310
    the 2 voltages
    170cos(2 Pi 60 t)
    170cos(2 Pi 60 t + Pi), 180 deg out of phase = -170cos(2 Pi 60 t)

    when summed around the loop starting at common
    v = 170cos(2 Pi 60 t) - (-170cos(2 Pi 60 t)) = 340cos(2 Pi 60 t)

    phasors
    120/0 = 120 + 0j
    120/180= -(-120 + 0j)
    sum = 240 + 0j = 240/0
    The difference between genius and stupidity is that genius has its limits.

  4. #14
    Join Date
    May 2011
    Posts
    4,131
    Quote Originally Posted by Ranes View Post
    ...

    Just to be clear, I understand how we can step down the higher single phase run (before transformer) from higher voltage primary to 240V and run a neutral to divide into 120V "pieces" on the secondary side, but what I can't find is some clarification as to why these are out of phase with each other. Is this something that just inherently happens when we tap a transformer with the neutral to get two 120V phases?

    Thanks for the help.
    I recall there was once a thread on this forum wherein a debate ensued as to whether the two 120V circuits were one phase or two phases and in phase with each other or not. It was basically semantics and the moderators decided that the conversation had gotten so stupid, or disrespectful, that they deleted the entire long thread. (Don't try to find it, you won't.)

    Practically speaking, if you were to scope both 120V legs, you could say your measurements are '180 degrees out of phase' if you keep the same probe on the neutral for both measurements, or you could say they are 'completely in phase with each other' if you were to swap the probe on the neutral. So calling them 'out of phase' is really just semantics, or at most a matter of choosing the correct mathematical expression for wherever you decide to point your probes. But sin(x) = -sin(x+180). Finally, remember that if you measure hot to hot, you are just measuring one waveform, and utilities call it a single-phase service. 'Two phase' power is actually something else, which is old fashioned and rare but still exists I guess in Philly and maybe a couple other places.

  5. #15
    Quote Originally Posted by gar View Post
    180511-1346 EDT


    Yes it inherently happens, if both halves of the secondary are wound on the same core, the secondary coil is one winding all wound in the same direction, and the center tap is in the center of the secondary winding.



    .
    Not to split hairs but.......

    The two halves of the secondary are NOT 'out of phase' (although it is impossible to tell this from looking at the wave-forms in this instance).

    They are OF OPPOSITE POLARITY, referenced to the center-tap.

    To demonstrate:

    Consider a complete cycle which consists of a positive going square wave for the first half-cycle, followed by a sine-wave second half of the cycle fed to the promary.

    If the two secondary voltages at 'L1' and 'L2' (the two 'output' terminals, referenced to the secondary center tap) were 180 degrees out of phase, each cycle at one of the 'L' terminals would have a square-wave first half, followed by a sine second half; the other 'L' terminal would have a sine first half followed by square-wave second half. Shifted a half-cycle in TIME, in other words.

  6. #16
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,094
    Quote Originally Posted by jaggedben View Post
    I recall there was once a thread on this forum wherein a debate ensued as to whether the two 120V circuits were one phase or two phases and in phase with each other or not. It was basically semantics and the moderators decided that the conversation had gotten so stupid, or disrespectful, that they deleted the entire long thread. (Don't try to find it, you won't.)
    Click here at your own risk

    Roger
    Moderator

  7. #17
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,310
    L1-n nd L2-n are 180 deg out of ph relative to each other
    this results in opposite polarity

    scope, com and 2 measuring probes
    com>n
    probe 1>L1
    probe 2>L2

    you will see 2 traces, mirrored

    reverse the winding on one coil and they will be in phase, 0 deg
    the traces will overlay

    if both were 120/0 then using kvl
    L1 = 120 + 0j....n to line is pos reference
    L2 = +(-(120 + 0j))....line to n is neg reference
    L1 + (-L2) = 0, which is not the case

    if L2 is 120/180 = -120 + 0j
    then L1 + (- L2) = 240 + 0j


    this does NOT make it 2-phase power
    The difference between genius and stupidity is that genius has its limits.

  8. #18
    Quote Originally Posted by Ingenieur View Post
    L1-n nd L2-n are 180 deg out of ph relative to each other
    this results in opposite polarity
    Sorry, no, that is backwards.

    They are of opposite polarity, which in this case is indistinguishable from a 180 degree phase shift.

  9. #19
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,310
    Quote Originally Posted by Gary Glaenzer View Post
    Sorry, no, that is backwards.

    They are of opposite polarity, which in this case is indistinguishable from a 180 degree phase shift.
    incorrect
    I have proven it mathematically
    the reason they are indistinguishable is because they are the same thing


    http://www.samlexamerica.com/support...chCircuits.pdf
    ** NOTE: The phase of Hot Leg 2 (Phase B) is in the
    opposite direction - i.e., 180° apart from the phase of Hot Leg L1 (Phase A)


    https://en.m.wikipedia.org/wiki/Spli...electric_power
    Current is transmitted in two sine waves, each of which is on its own "hot" wire, and each of which varies between +120V and -120V with respect to ground. Because the waves are 180° out of phase with each other, this means that when one is at a full +120V, the other is at full -120V, for a difference of 240V; both reach 0V at the same time. When added together, this results in a circuit which varies between +240V and -240V with the same frequency, but "split" across two hot wires rather than one hot and one neutral.
    The difference between genius and stupidity is that genius has its limits.

  10. #20
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,310
    one of you guys with a scope
    how about trying this
    neut to common
    L1 and L2 to seperate measuring probes

    what is the time delta between pos peaks (or ascending 0 crossings)?

    close to 8.333 mSec?

    1/60 sec = 360 deg so 1/120 sec = 180 deg
    The difference between genius and stupidity is that genius has its limits.