    The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,070
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jennifer K. View Post
    Could be several things.
    EGC. Bonding jumper of some kind. Might even be a GEC.
    Is the switchboard really the service point?
    I don't know what you mean by main building ground bar.
    Bob
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,641
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    GEC.
    Rob
  4. #4
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,331
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Most of my designs place the N-G bond inside the service switchboard. A ground wire from the neutral bar in the direction of planet Earth (via the bus bar on the electric room wall) is a GEC.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  5. #5
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,033
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    From Mike Holt "What color is it and what does it do?"
    Most call it a ground which means nothing.
    Moderator-Washington State
    Ancora Imparo
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    More details on what this "main building ground bar" is critical to the answer.
    If it is a place for multiple services to tie together and then connect the grounding electrode system to it - each connection to each service is a bonding jumper I would think.
    If it is a place for other systems to be able to connect grounding/bonding conductors to - I'd still say it is a bonding jumper but doesn't necessarily need to be sized the same way as the other condition I mentioned.
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,070
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    250.30(A)(6) calls it a grounding electrode conductor tap.
    Bob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    Ok thanks. I was aware of what that section allows, but did not look to see if they gave a name to such a conductor. Sort of a name that only applies to that section and not a name that applies to the NEC in general or even art 250 in general - or it would probably be in art 100 or 250.2.
  9. #9
    Join Date
    Mar 2003
    Vermont
    Posts
    1,959
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Where is the MBJ?
    ~RJ~
  10. #10
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The building ground bar is an extension of the grounding electrode system therefore an external grounding conductor form the switchboard is most likely the GEC.