    next higher size???

    Hi
    I am supplying a 120' away sub panel l thru a set of #6 thhn, cu in an apartment building.

    Question is,
    can use 70A ocpd for the feeder main ; according to next-larger size rule ?????

    Also,
    70A ocpd for the feeder main; What size copper wires can be used to feed that apartment sub panel. ???????

    Thank you

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,182
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    215.2 requires that your feeder conductor have the amapcity to supply the load so your #6 THHN would be good for a 65 amp loadassuming 75° terminations. If your load does not exceed 65 amps, you are good with a 70 amp overcurrent device.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    215.2 requires that your feeder conductor have the amapcity to supply the load so your #6 THHN would be good for a 65 amp loadassuming 75° terminations. If your load does not exceed 65 amps, you are good with a 70 amp overcurrent device.
    I second that and add that if your feeder is NM cable - you are limited to 60C ampacity.