User Tag List
Results 1 to 5 of 5
Thread: Shared Grounding Electrode System with separate structure
  1. #1
    Join Date
    Feb 2007
    Alexandria, VA
    Posts
    430
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I am always looking for a way to avoid driving ground rods!
    I have a separate structure (workshop with no water) about 20 feet from the house meter/panel.
    Can I run a #6 from the panel in the workshop back to the house GES thus avoiding driving two more rods?
  2. #2
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,043
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Short answer, No
    If you aim at nothing, you will hit it every time!
  3. #3
    Join Date
    Sep 2005
    Greenville SC
    Posts
    766
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    what if it is slab on grade with steel which might qualify as a ufer ... perhaps easy if yet to be built?
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,044
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GeorgeB View Post
    unless the slab has a foundation there is no CEE and thus not a valid GE according to the NEC.
    pound a few ground bars and be done with.
    Bob
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,595
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If you can meet the requirements for a CEE in the footings then you won't need ground rods.
    Rob