Hi everyone and thanks for looking at this post. I am on the 2011 NEC code and have a system with 3x Fronius Symo 12.0-3-Delta inverters. Each inverter has an output of 33.3 A at 208V. Each inverter is going to a solar subpanel and connected to 3x 50A 3 pole breakers. The bus on the subpanel is 400A and the MCB is 150A. My question is, do I have to size my wire running from the MCB to the MDP breaker according to the size of the MCB or the total output of the inverters? Essentially, does the wire need to carry 150A or can I get away with a wire that only carries 100A since 33.3 x 3 = 99.9.:?
 

Carultch

Senior Member
Location
Massachusetts
Hi everyone and thanks for looking at this post. I am on the 2011 NEC code and have a system with 3x Fronius Symo 12.0-3-Delta inverters. Each inverter has an output of 33.3 A at 208V. Each inverter is going to a solar subpanel and connected to 3x 50A 3 pole breakers. The bus on the subpanel is 400A and the MCB is 150A. My question is, do I have to size my wire running from the MCB to the MDP breaker according to the size of the MCB or the total output of the inverters? Essentially, does the wire need to carry 150A or can I get away with a wire that only carries 100A since 33.3 x 3 = 99.9.:?

You have the continuous load factor on this, which means you'd need 125A worth of wiring by default, prior to considering the wire protection.

If you are using a 150A breaker, you need at least 126A worth of wiring. Essentially, it must exceed the previous breaker size, so that the wire's ampacity rounds up to the next standard breaker that you are using. See 240.4(B).
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
In my opinion you can size your breaker and wiring for 125A instead of 150. It is still an output circuit required to be sized to 125% of the output, but you can base it on the combined output of the inverters and not the breakers that protect them.

With respect to the busbar for the combiner panel, an AHJ might require the busbar to be (150+125)/120%.

Incidentally 45A is a standard size, although whether you can find 45A 3-pole breakers is another question.
 

Carultch

Senior Member
Location
Massachusetts
In my opinion you can size your breaker and wiring for 125A instead of 150. It is still an output circuit required to be sized to 125% of the output, but you can base it on the combined output of the inverters and not the breakers that protect them.

That is the case, if you are only using as large of a breaker sized as large as you need. If you are using a breaker in excess of what you need, you need at least as much ampacity as the previous standard breaker (with a fraction of an ampere greater). See 240.4(B).

So if you choose to connect this to a 200A breaker, instead of 125A as you need per the 125% rule, you'd need at least 175.000001 Amps of wire. This is the case if you have an overcurrent device that is required. If an OCPD isn't required, but is there anyway, you can treat it as if it isn't there, and it wouldn't affect wire sizing.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
That is the case, if you are only using as large of a breaker sized as large as you need. If you are using a breaker in excess of what you need, you need at least as much ampacity as the previous standard breaker (with a fraction of an ampere greater). See 240.4(B).

So if you choose to connect this to a 200A breaker, instead of 125A as you need per the 125% rule, you'd need at least 175.000001 Amps of wire. This is the case if you have an overcurrent device that is required. If an OCPD isn't required, but is there anyway, you can treat it as if it isn't there, and it wouldn't affect wire sizing.

Point taken, although in this case it seems he would need to use #1 copper at 130A and the difference between a 125A and 150A breaker is moot. I overlooked that the OP said he was using a 150A breaker; I thought he was asking after the smallest breaker he could use as well as the wire. I'd use a 125A breaker myself.

I'm curious why you say the wire ampacity must be a millionth of an amp over the breaker rating, instead of a thousandth or a billionth. :p
 

Smart $

Esteemed Member
Location
Ohio
... 175.000001 Amps of wire. ...
The NEC does not require significant digit rounding for calculations... but it should. :happyyes:

I always go by 220.5(B) rounding >0.5 up and lesser fractions down... so a 126A ampacity minimum (because ampacity is only given in whole number values) would be required to use a 150A breaker.
 

Carultch

Senior Member
Location
Massachusetts
I'm curious why you say the wire ampacity must be a millionth of an amp over the breaker rating, instead of a thousandth or a billionth. :p

It was arbitrary. I just held the zero key down a random amount of time, and it happened to coincide with a millionth. I'm exaggerating to make my point about the next size up rule, in the sense that the ampacity of the conductor cannot be an exact match to the previous standard OCPD rating, and that it has to be able to exceed the previous and round up to the next. The rule doesn't specify just how much it needs to exceed the previous standard size.

I've been in situations where after adjustment and correction factors, the ampacity of the conductor is small fractions (less than 0.5A) of amperes above a standard breaker size. It can also depend on how you calculate the temperature correction, whether you use the square root formula, or the rounded values based on the 5C temperature ranges.
 

roblsmith3

Member
Location
Cary, NC USA
Thank you all for replying! I originally had 1 AWG and wanted to be sure it was still good to use. JaggedBen, i hear you on the 125A MCB thing.....That's what I would like to do but a lot of the AHJs around here don't see it that way and want us to add up the breakers.....I've been fighting it for years! Anyways, thank you all again for replying. Till next time!
 

Carultch

Senior Member
Location
Massachusetts
Thank you all for replying! I originally had 1 AWG and wanted to be sure it was still good to use. JaggedBen, i hear you on the 125A MCB thing.....That's what I would like to do but a lot of the AHJs around here don't see it that way and want us to add up the breakers.....I've been fighting it for years! Anyways, thank you all again for replying. Till next time!

Do they ever provide a code reference on why they want you to add up the breakers, and accumulate all the rounding errors? Instead of adding up the current, and applying a master 1.25 factor. The AHJ is not supposed to make up their own rules. Any violation claim needs to be based on a specific code requirement.

I can understand accumulating rounding errors, if you are sizing conductors for use with an MLO panel with no master OCPD anywhere within the main output circuit. But once you have a master OCPD, the master OCPD should only need to be as large as 125% of the total maximum continuous current, and the wire should only need to be as large as needed for the load and to be protected by the master OCPD.
 

Smart $

Esteemed Member
Location
Ohio
That's only true for calculating the 120% rule. The code never said that the breaker for a feeder supplying an AC combiner has to be done that way.
Some interpret the 120% rule of earlier editions as applying to all buses and feeders between PV inverter and service.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Some interpret the 120% rule of earlier editions as applying to all buses and feeders between PV inverter and service.

Yes, but still not the breaker for the feeder. Some AHJs will apply it to all busses and conductors, and some will apply it to none if the bus is in a combiner panel dedicated to inverters. Most the AHJs I encounter will not apply it to the feeder even under the 2011 code.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
. The AHJ is not supposed to make up their own rules. Any violation claim needs to be based on a specific code requirement.
The AHJ can adopt the NEC or not, and it can selectively enforce it as well as amend it as they see fit. My local AHJ has adopted the 2014 NEC but is not yet enforcing rapid shutdown. The AHJ is the last word.
 

iwire

Moderator
Staff member
Location
Massachusetts
The AHJ can adopt the NEC or not, and it can selectively enforce it as well as amend it as they see fit. My local AHJ has adopted the 2014 NEC but is not yet enforcing rapid shutdown. The AHJ is the last word.

I doubt that is true in your area and it certainly is not the case in most places.

That would be the same as a judge making up laws on the spot.
 

Smart $

Esteemed Member
Location
Ohio
Yes, but still not the breaker for the feeder. Some AHJs will apply it to all busses and conductors, and some will apply it to none if the bus is in a combiner panel dedicated to inverters. Most the AHJs I encounter will not apply it to the feeder even under the 2011 code.
You are correct. Got to thinking about it after I posted. Figured I'd wait until you replied to 'fess up.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I doubt that is true in your area and it certainly is not the case in most places.

That would be the same as a judge making up laws on the spot.
The city passed an ordinance that declares what is the electric code for the city. It references the 2014 NEC but adds stuff that is not in the NEC. They don't make stuff up on the spot but they enforce their code, which is mostly the NEC but has some differences. The NEC is not law but their ordinance is.
 

iwire

Moderator
Staff member
Location
Massachusetts
The city passed an ordinance that declares what is the electric code for the city. It references the 2014 NEC but adds stuff that is not in the NEC. They don't make stuff up on the spot but they enforce their code, which is mostly the NEC but has some differences. The NEC is not law but their ordinance is.

Yes, same in many places

The AHJ makes written changes that everyone know about, they cant simply decide on the spot.
 