    Single Phase Transformer Secondary Grounding

    Hi,

    I have a singles phase 1.5Kva transformer, 480VAC 1ph primary to 120VAC 1ph secondary. H1 and H4 are my primary lines, H2 to H3 connected together. X1 to X3, X2 to X4 and secondary lines to X1, X4 for 1ph 120VAC. My question is, does any of the secondary need to be connected to ground? I know have seen some secondary 120VAC, 1ph be 180 - 190VAC.

    Thanks,
    Kilowatt

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,615
    Yes you need to install a system bonding jumper and a GEC.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Mar 2015
    Location
    Rock Hill, SC US
    Posts
    11
    Quote Originally Posted by infinity View Post
    Yes you need to install a system bonding jumper and a GEC.
    So, I need to connect a ground wire to X2 and X4?

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,857
    Quote Originally Posted by Kilowatt76 View Post
    So, I need to connect a ground wire to X2 and X4?
    You need to bond X2/X4 to the EGC and run a GEC to the nearest qualifying GE connected to X2/X4. often there is a stud on the transformer case for this.
    Bob

  5. #5
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,973
    It's a separately derived system that falls under 250.21. You can elect either secondary conductor to be the grounded conductor and, as infinity states, bond that conductor and connect it to a grounding electrode as specified in 250.30
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  6. #6
    Join Date
    Mar 2015
    Location
    Rock Hill, SC US
    Posts
    11
    Got it, thank you guys!

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,543
    Quote Originally Posted by petersonra View Post
    You need to bond X2/X4 to the EGC and run a GEC to the nearest qualifying GE connected to X2/X4. often there is a stud on the transformer case for this.
    Unless there are specific instructions that state to do so on x2/x4, NEC is fine with grounding either secondary conductor.

    If one were using 120/240 volts on this secondary then NEC requires grounding the "neutral" which is going to be X2/X3 connection.
    I live for today, I'm just a day behind.

  8. #8
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,857
    Quote Originally Posted by kwired View Post
    Unless there are specific instructions that state to do so on x2/x4, NEC is fine with grounding either secondary conductor.

    If one were using 120/240 volts on this secondary then NEC requires grounding the "neutral" which is going to be X2/X3 connection.
    The OP indicated X2 and X4 were connected together. that would make sense for a 120V secondary, as opposed to a 240/120 V secondary.
    Bob

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,543
    Quote Originally Posted by petersonra View Post
    The OP indicated X2 and X4 were connected together. that would make sense for a 120V secondary, as opposed to a 240/120 V secondary.
    Yes, NEC doesn't care if you ground X1/X3, or X2/X4. Neither one when used in that configuration is "neutral".
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,198
    It's funny how often it seems "scary" to ground a conductor that doesn't enter the building already so grounded.