    So I’m upgrading a motel to support 42kW of added heating load. The units are all 240 1ph. I figured 350 awg cu. for the hots. I should be able to reduce the neutral by 80% right? If so how do I calculate that? What starting point do I use to apply the 80% to?
    Tell me and I forget. Teach me and I remember. Involve me and I learn.
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    208/240v ptacs and a/c units dont use a neutral at all.
    42kw is a very small upgrade.. are they changing 9kw ptacs to 12's? Few Panasonic units to the lobby or hallways?
  3. #3
    Join Date
    Jun 2014
    Madison, WI, USA
    Posts
    358
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    These are cadet 3000w wall heaters. I know they don’t use a neutral. That’s why I want to reduce the neutral for the new service but I’m wondering what I apply the 80% to
  4. #4
    Join Date
    Dec 2011
    Wisconsin
    Posts
    560
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by DrSparks View Post
    Look at 250.24(C). The grounded conductor cannot be smaller than the required grounding electrode conductor. For 350 kcmil copper the neutral cannot be smaller than a 2 AWG.
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What 80%?
    Grounded service conductor can be as small as the required GEC if the neutral load isn't there.
    Comes down to what is maximum unbalanced load that may be present on the neutral?
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Jun 2014
    Madison, WI, USA
    Posts
    358
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Idk I need to reread the whole service call section. I thought I read somewhere about 80% max reduction for neutral. I’m probably going to have to do a load calc for this place. Makes sense about the neutral being no smaller than GEC has to be able to handle short circuit. Got it
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    See 250.24(C). Note: 230.23(C), 230.31(C) and 230.42(C), all reference this section for minimum size.
    Actually minimum size is same as minimum supply side bonding jumper though it is same size as minimum GEC in many instances.
    310.15 will require them to be able to have ampacity to handle maximum current they are subjected to, with adjustments where they apply.
  8. #8
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,250
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ]I thought I read somewhere about 80% max reduction for neutral.
    If I'm not mistaken, you're referring to the allowance to reduce a neutral TO 80%, not BY 80%, of the line conductors' capacity.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  9. #9
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,182
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    don't know what size service you plan but, FWIW, 350 kcmil is about twice the size needed for the load.