    Can a single Ground Rod be used to Bond more than 1 transformer?
    I'm installing a new 480-208/120 transformer to feed a Loadcenter; there's a Ground Rod next to this installation used with another transformer.
    Can I Bond the new transformer to the existing Ground Rod?
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,153
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I don't know of any reason why you cannot use a ground rod for both transformers. Is one rod enough?
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,070
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by dasarmin View Post
    Unless it has been tested to show the ground resistance < 25 Ohms two ground rods are required.
    All grounding electrodes associated with a single structure have to be bonded together.
    When you create a new SDS it has to be connected to the structure's grounding electrode system (GES).
    250.30 is the answer.
    Bob
  4. #4
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,153
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I think the post may be confusining. If there is only one rod then the first transformer probably needs 2- rods at least 6' apart and bonded together. Then, you can use those same rods for the second transformer also.
    I
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Neither transformer needs to connect to a rod.
    They need to tie into the grounding electrode system, which 480 volt system that supplies the transformer should already be connected to. Even if you desire to add additional rods or other electrodes for whatever reason - they still need to also be bonded to the GES.
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    Just a note - 2017 NEC changed the definition of 'Structure' to; "That which is built or constructed, other than equipment."
    I take this to mean, pump, skid and transformer pads no longer require bonding of rebar.
  7. #7
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    I
    I know the Code requires 6 feet separation for supplemental electrodes (rods) however rods are frequently driven one on top of the other to achieve 25 ohms. The average, single ground rod in the US is about 40ohms.
  8. #8
    Join Date
    Feb 2003
    Fl
    Posts
    17,481
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dale001289 View Post
    Please provide the source of that statistic.
    Roger
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    Roger
    Mastering the NEC - Mark Shapiro
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The ones driven one on top of the other are coupled together to create a single longer rod aren't they? You can't do this with the typical 8 foot rod without some sort of coupling method be it integrated into a rod or an additional fitting.
    40 ohms average is nothing more then trivia information. Doesn't mean if I go outside my front door and drive a rod there it will be 40 ohms.