    I can't seem to find a clear answer here, but I think I am correct in saying that if 2 people "dwell" in a cell separate from the common area in jail and they have a receptacle in their cell which is within 6 ft. of a prison toilet/sink combo unit wouldn't it be required to GFCI protect it? There are GFCI breakers installed already, but they seem to be troublesome. My main question is it required and I think it is. Any feedback would be great. Thanks.
  2. #2
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,725
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A prison cell is not a dwelling unit, IMO.
    That said, the outlet being within 6' of the sink requires GFI protection. Depending on when the building was built.
    I can't remember what code cycle started to require GFI protection for outlets w/i 6' of sinks in other than dwelling units.
    Ron
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rcarroll View Post
    I agree. Prison cell typically has most of items needed to be dwelling unit per NEC, but probably very rare for one to have provisions for cooking.
    I live for today, I'm just a day behind.
  4. #4
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    1,139
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I thin it was almost a life sentence ago?
  5. #5
    Join Date
    May 2009
    Posts
    24
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This jail was built in the early 80s around 1982 or 1983 so according to this thread they were required in dwelling bathrooms and fountains. Being a pre-existing condition it is ok to say that it's not required unless a new circuit was installed? The only thing they might be able to use are clippers near the sink. So we agree that one it's not a dwelling unit and two GFCI in this location was not required when this building was constructed? Thanks for all the input.
  6. #6
    Join Date
    Apr 2018
    newengland
    Posts
    24
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by buffnitup View Post
    "prison cell" needs to be defined. There are cells and there are rooms. I don't think that "clippers" would be allowed in a cell.
  7. #7
    Join Date
    Apr 2005
    Atlanta,GA
    Posts
    6,037
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would think that if GFCI protection is required (6 ft. of sink) then either a GFCI breaker or GFCI receptacle would be required if the receptacle is changed out after the code requirement.
    The 95% of people that you can't trust give the other 5% a bad name.
  8. #8
    Join Date
    Apr 2005
    Atlanta,GA
    Posts
    6,037
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mortimer View Post
    What's allowed would have more to do with security requirements. This may not be a maximum security facility.
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by growler View Post
    I agree, change out situation can make you install if now required even if it was compliant at original installation time.
  10. #10
    Join Date
    Jun 2003
    Posts
    6,947
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I'll third or 4th that. GFCI required. I'm thinking sink, clippers, and barefoot inmates with a bare concrete floor - I wouldn't want to omit the GFCI.
    But I guess putting in a GFCI receptacle in the cell is a problem due to possible vandalism, or similar issues? If the GFCI breaker have a problem tripping, they might be too far away from the receptacles (too much wire length).
    Maybe a deadface GFCI could be located closer to the receptacles? ALso, is there anything else wired to the GFCI breaker? Maybe lights?