    Quote Originally Posted by charlie b View Post
    The "well" is about 8' x 8' x 18'. The pump is in the sump, but the motor is 45' above the pump, and a very long shaft connects them.
    575V motors are not real hard to get. my guess is that given the nature of the project it is likely they will get a spare motor anyway.
    Bob
  2. #42
    Join Date
    Dec 2008
    Posts
    549
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In my opinion, 3*#4 [compact stranded conductor,0.64 sq.in] is the maximum power cable
    allowed to pass through 1-1/4" RMC.
    If the conduit is embedded under 3 ft in concrete and 90 RHO soil 3*#4 copper conductor could withstand 103 A as per IEEE 835/1994 IEEE 835/1994- 0.6 to 5 kV Unshielded Single Conductor Extruded Dielectric Cable in Underground Duct Bank - Triplexed - Single Circuit
    25ºC Earth Ambient 90oC insulation rated table.
    Let's say the pump works 1 hr and 0.5 hr pause.Then Iav=sqrt(1*124^2/1.5)=101.25 A
    Another solution: a parallel cable of 3*#4 copper along the same path.
    It is not a beautiful solution but it could work for a while.
  3. #43
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,185
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Julius Right View Post
    Not only would it not be beautiful, it would not be legal (can't parallel less than 1/0)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  4. #44
    Join Date
    Dec 2008
    Posts
    549
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree with you, augie47.A better solution, if there is a free path, to cancel the 3*#4 cable and run along the same path a suitable cable for ampacity and for voltage drop reason.
  5. #45
    Join Date
    Feb 2013
    India
    Posts
    2,550
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks, JR. As for any unequal spacing in the triplex cable, any voltage unbalance at the 100 hp pump motor?
  6. #46
    Join Date
    Dec 2008
    Posts
    549
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As far as I know, triplex means that single-core cables are tied together so the center-to-center distance is the same. I think you intend to say separately laid single-core cables inegal distanced. The voltage drop depends on resistance and reactance -differences it could be if the phase length is different.The center line distance difference does not produce phase voltage drop difference.
    X=2.π.f(0.1404log10(S/r)+0.0153)x10^(-3) ohm/1000'
    Equivalent spacing S=(A*B*C)^(1/3) it is the common equivalent S for any of the phases.
    Name:  Triplex cable.jpg
  7. #47
    Join Date
    Apr 2006
    Springfield, MA, USA
    Posts
    3,426
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Using compact stranded copper conductors, the minimum EGC for the available circuit size, and 600V, what is the maximum power that could be delivered in a 1-1/4 rigid conduit?
    I think you get 3x 1/0 AWG + 1x 6AWG
    This gives 150A of ampacity, and continuous loading of 120A. 125 kW
    If you use larger gauge tails and 90C splices (to get the 90C ampacity of the wire in the conduit) and use 100% rated circuit protection, then you get 170A and 177kW capacity.
    There has to be some way to work the requirements to operate a 75kW motor into conductors with more than double that capacity!
    -Jon
  8. #48
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by winnie View Post
    -Jon
    Use the raceway as EGC and you can get 3 -2/0 compact THHN in 1.25" RMC.
    I live for today, I'm just a day behind.
  9. #49
    Join Date
    Dec 2008
    Posts
    549
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you intend to use XHHW cables-the insulation thickness it is only 55 mils- then you are right.
    3*1/0 it could pass through. 3 conductor cable it is not a NEC cable but a UL 44 and it is provided with insulation of 55 mils and overall jacket of 80 mils. I am not sure XHHW may be use for pump supply.
    However 3*#2 conductor cable-it seems to me- may run through 1-1/4 RMC.
    For this cable IEEE 835/1994 allows 136 A[90oC insulation,90 RHO,25oC Earth, copper conductor,100% L.F.]