    Quote Originally Posted by electrofelon View Post
    He might want to see if this is actually a local amendment vs something the inspector "wants"
    Agreed. And kwired, could be, tho many use AHJ and inspector interchangeably when they really arent. I see nothing wrong with using three wire ranges and dryers, within the provision of 250.140. There are literally millions of homes that have them installed, with aluminum wire SE cable) at that, with no problems.
    Here, if you move the receptacle, it is no longer "existing", and then you don't meet 250.140. Changing a main panel into a subpanel would require a 4 wire feed to both ranges and dryers.
    Unless, like electrofelon wrote, this is a local amendment in the original posters area, I would definitely fight this one.
  2. #12
    Join Date
    Feb 2003
    San Jose, CA
    Posts
    1,553
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Maybe I missed it........ but what wiring method is currently being used to supply the dryer?
    Curt Swartz
    Electrical Contractor
  3. #13
    Join Date
    Mar 2003
    New England
    Posts
    13,851
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We extended a 3-wire circuit the other day for a 4-wire oven. Last I checked the sun still came up and went down.
  4. #14
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,030
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by curt swartz View Post
    Don't think it was really mentioned - but most likely is safe to presume NM or SE cable.
    I live for today, I'm just a day behind.
  5. #15
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,207
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    OP said 10-2
    If you aim at nothing, you will hit it every time!
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,030
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    OP said 10-2
    Actuaally he said the water heater next to it he would like to connect the EGC to is supplied with 10-2, NM cable.
  7. #17
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,336
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree NEC doesn't require the change - but I think he is saying they have a local rule that says it must be changed if the service is upgraded. IMO, dumb rule. NEC allowing these three wire circuits (at least as long as they did) was dumb as well though. This is a little like buying an older car but a local authority says you must equip it with current model year required safety features or you can't drive it on a public road.
    Quote Originally Posted by JFletcher View Post
    Yes, this is a local rule. I've never actually spoken to the chief electrical inspector about it, but multiple underlings have said this is true. I think I will have to call and ask the chief just to be sure.
  8. #18
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,336
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The water heater is wired with modern orange 10-2 NM. The dryer is currently wired with 3-wire, no ground, cloth covered cable (also NM I believe).
  9. #19
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,336
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Anybody have an answer to the question in post 7?
  10. #20
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,207
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Actually, you have too may vowels in actually