    Arc fault in main panel tripping due to grounds and neutrals bonded

    Could the arc fault breaker be tripping due to the neutrals being bonded in a main panel? The breaker is a GE pigtail stab in type


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,171
    Quote Originally Posted by redeemed1 View Post
    Could the arc fault breaker be tripping due to the neutrals being bonded in a main panel? The breaker is a GE pigtail stab in type


    Sent from my iPhone using Tapatalk
    No. the load side of breaker neutral needs to fault to ground for "ground fault" trip feature to be the reason for the trip. The panel neutral bus even though it is bonded at a service panel is on the supply side of the AFCI device.
    I live for today, I'm just a day behind.

  3. #3
    Join Date
    Jul 2015
    Location
    austin,tx.
    Posts
    7
    Quote Originally Posted by kwired View Post
    No. the load side of breaker neutral needs to fault to ground for "ground fault" trip feature to be the reason for the trip. The panel neutral bus even though it is bonded at a service panel is on the supply side of the AFCI device.
    Thank you